Hi guys,

weve been having trouble identifying the supply supply type at a building were we are carrying out the installation of EV charge points and it's obviously important we get it right as it will derermine wether we have to install earth electrodes for the charge points.

it is a large newly built commercial building with a 3 phase 4 wire supply. On first glance it seems to be a PME system, the bolt on the side of the service heard is linked to the neutral bar inside, however there is also a separate 70mm Earth coming in with the main cable (I assume comes from the transformer) terminated to the same bolt.

Is it possibly both supply types are present and we don't need to install electrodes? Cheers in advance
 
How can it be TNC-S and TN-S if the separate earth conductors connection point is connected to the neutral at the service head?? The separate earthing conductor is far more likely to come from a local earth rod than a TN-S source earth!!

You can safely say that this installation is a 3 phase PME/TNC-S system....
 
Could it be PNB with the 70mm earth being the earth electrode?

Or maybe an additional earth electrode on a PME supply.

Have you tried asking the DNO?
 
Could it be PNB with the 70mm earth being the earth electrode?

Or maybe an additional earth electrode on a PME supply.

Have you tried asking the DNO?

Not at a DNO consumers service head it won't be!! That's what you'll see at a TX or maybe at the TX's LV main switchboard.
 
Thanks for the replys, I'm going to contact electricity North west on Monday, never done this before so not sure how easy it will be to get in contact with someone who has a definitive answer. I was sure it was a PME system at first glance but then couldn't find an explanation for the incoming 70mm Earth, depending where that Earth is from it can make a big difference to our installation, it won't be easy to install the earth electrodes if they are required
 
Thanks for the replys, I'm going to contact electricity North west on Monday, never done this before so not sure how easy it will be to get in contact with someone who has a definitive answer. I was sure it was a PME system at first glance but then couldn't find an explanation for the incoming 70mm Earth, depending where that Earth is from it can make a big difference to our installation, it won't be easy to install the earth electrodes if they are required

Now i'm totally confused, why will this make a big difference to your installation, if you were already sure it was a PME supply?? So what's changed?? You would have known that earth electrodes would be required for this commercial multi EV charging point installation....

So where do you think this 70mm earth conductor is coming from, and what difference do you think it's going to make for your installation??
 
Now i'm totally confused, why will this make a big difference to your installation, if you were already sure it was a PME supply?? So what's changed?? You would have known that earth electrodes would be required for this commercial multi EV charging point installation....

So where do you think this 70mm earth conductor is coming from, and what difference do you think it's going to make for your installation??

Hi E54, please correct me if I'm wrong, but as I understand it the separate Earth electrodes are required in case the neutral conductor fails then a person would be the path to Earth in the event of a fault, however on this installation if the neutral conductor did fail and there was a fault condition the 70mm Earth would still provide the path to Earth, if it's coming from the transformer, or even from another electrode.
 
Hi E54, please correct me if I'm wrong, but as I understand it the separate Earth electrodes are required in case the neutral conductor fails then a person would be the path to Earth in the event of a fault, however on this installation if the neutral conductor did fail and there was a fault condition the 70mm Earth would still provide the path to Earth, if it's coming from the transformer, or even from another electrode.

Correct... A local earth electrode system connected to the MET or to the Neutral connection itself will greatly reduce the adverse effects of an extremely rare scenario of a broken neutral. If the Ra value of that electrode system is very low and at the very least complies with DNO values which as i remember is below 5 or 10 ohms... It's basically just another N-E connection on a ''Protective Multiple Earth'' system, albeit being locally provided. Very common on larger DNO 3 phase installations of say 400A and up...


If this was a single domestic EV charging point you were installing, i would be telling you not to bother about the supply being PME or not. But as i understand it this is a commercially based installation so a TT system will need to be provided for the multiple EV charging points...

EDIT.... If as you say there is a Transformer in this building or on the property, then the 70mm could well be coming from the transformers LV's main distribution boards earthing system. but everything still remains the same, it's still a PME/TNC-S supply you have there.
 
Last edited by a moderator:

Reply to TN-S or TNC-S or both?? in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
945
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
Hi all, I've recently had 2 customers enquire about installing a backup generator for their domestic premises. After a lot of research...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock