Discuss Tripping Shower in the Electrical Appliances Forum area at ElectriciansForums.net

Crannoid

DIY
Reaction score
1
I have a 9.5kw shower running from a 40 amp rcb. About 10 minutes after turning the shower off the rcb trips. This has only just started, the shower has been in since we moved in. There is no pull cord switch, or rocker switch for the shower.
Any thoughts why this might be happening?
 
yes,
9.5kw at 230V is 41.3A
it is only a slight overload but will eventually trip the rcd.
they might have got away with it whilst it was new and all the springs in the breaker were at there peak performance.

have a look at the instructions for the shower and see what supply requirements are.
I suspect it is an under rated supply.
 
Welcome to the forum mate.
As above, are you sure it's the RCD tripping and not the MCB?
The RCD tripping would imply a fault with shower or cable to the shower. Maybe some water is leaking into the shower....
I can't imagine a MCB tripping after the shower has been switched off for 10 mins from an overload point of view... Again water ingress into the shower may cause this.
 
my first thought would be that the MCB has been running at it's limit for so long, it's just got fatigued. get a local spark to replace with a 45A cartridge fuse. ( unless he can source a 45A MCB.).
 
CGD/Lewden stuff only has MCB and RCBO current ratings of 40 or 50Amps, no 45Amp.

Very strange it trips after 10 minutes of being off. I'd be visually checking inside the shower for leaks or burnt stuff first.
 

Reply to Tripping Shower in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
964
my client has just purchased a 8 kw power shower, i have watched a youtube video on how to run the pipe work so i think i have that figured out...
Replies
11
Views
1K
Hi, after a bit of advice. Have tried a lot of plumbing and electrical shops but no one seems able to help. I have an Isolator/PSU 230v/12v. It is...
Replies
11
Views
871
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
280
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock