Hi guys,

after some advice please.

Been asked to install electrics for an underfloor heating system that consists of 3 x 10m2 mats, at a maximum rating of 2400 watts per mat, ran off the one thermostat (max 16amps).

Has anybody ever wired this system using a 40amp contactor?? And if so all help would be gratefully appreciated. (diagrams)

thanks
 
pretty straightforward,the thermostat switches the contactor coil on and the contactor contacts switch the power to the mats
 
  • Like
Reactions: 1 person
Thanks,

Would i be correct in saying i would supply the contractor with a 10mm2 cable. then supply the 3 individual mats with a 2.5mm t&e and joint in a junction box.
 
out of interest where do you plan to "conceal" the contactor and the cables? Last one I saw like this the contactor was in a 47mm deep back box, mounted "portrait", behind a 2G blank! A right dogs dinner!
 
Thanks,

Would i be correct in saying i would supply the contractor with a 10mm2 cable. then supply the 3 individual mats with a 2.5mm t&e and joint in a junction box.

No you wouldn't be correct! The 2.5 would then not be protected.

The last time I did this I ran 3x 10A circuits switched with a 3 pole contactor.
 
  • Like
Reactions: 2 people
Have a long hard think about what contractor your using and where it's going to be positioned, if it's not going to be out of ear shot of the home owner consider a silent switching one to lower the chance of having to move it. What may seem quite during the day can be very loud at night when the heating is switching on and off.
 
  • Like
Reactions: 2 people
No you wouldn't be correct! The 2.5 would then not be protected.

The last time I did this I ran 3x 10A circuits switched with a 3 pole contactor.

Same arrangement last time I did one.

Post #3 is a worry.

Also worth pointing out to the end user just how much this will cost to run per hour.
 
Worth considering the length of the tail to the mat to be able to have everything concealed but also not not making anything inaccessible, because if it's just 3 x mats laid down then they will all have their own individual supply and they will all be at different points within the room, check with manufacturers instructions that they can be ran via a stat controlling a contactor, the ones I've done in the past have a stat in the floor and run via a controller that has the stat input and mat output in it.
 
Worth considering the length of the tail to the mat to be able to have everything concealed but also not not making anything inaccessible, because if it's just 3 x mats laid down then they will all have their own individual supply and they will all be at different points within the room, check with manufacturers instructions that they can be ran via a stat controlling a contactor, the ones I've done in the past have a stat in the floor and run via a controller that has the stat input and mat output in it.
Of course it can be run via a contactor, its no different to connecting it directly to the stat!
 
  • Like
Reactions: 1 person
I understand that, but manufacturers instructions need to be complied with for warranties etc!
 
If the installation isn't installed as per the manufacturers say it should be, if they send a rep out and it differs from the instructions and there is a problem they will probably wash their hands, I've seen it happen, that's why I commented about it. But, crack on and install things as you want as it's just my opinion!
 
If the installation isn't installed as per the manufacturers say it should be, if they send a rep out and it differs from the instructions and there is a problem they will probably wash their hands, I've seen it happen, that's why I commented about it. But, crack on and install things as you want as it's just my opinion!

What on earth is a rep going to know?

Which underfloor heating manufacturer was it when you saw it happen?
They would have to be able to prove that whatever fault has occurred could be due to the deviation from their instructions, and there's no way adding a contactor could do that. It's far more likely that the manufacturer would bull**** their way out of it by baffling a customer who is too daft to think for themselves with that nonsense.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Under floor heating
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
MATTMGM,
Last reply from
Lagentium,
Replies
13
Views
1,560

Advert