if your R1+R2 readings came back as satisfactory then that circuit impedance should be OK. Therefore you need to start looking at other factors relating to this issue i.e your Ze!! Are you earthing conductors connected correctly and secure and in good condition?

Get another rod sank in and see if this is any better to lower your Ze
 
ZE was 187

the system is protected by a 30ma RCD from the main house, and the new board is also protected by a 30 ma RCD.

??


Ok then your maximum allowed Zs reading for each 30mA protected circuit is 1667 Ohms, problem solved in 31 posts.

Your RCD at the supply end should ideally be an 'S' type time delayed to achieve discrimination with the RCD at the remote end but I wouldn't loose sleep over that one.
 
ZE reading 187ohm

I can determine ZS by enquiry, ZE +R1 +R2 = ZS

However, i tried to test and measure ZS at the end of the circuit and got these high figures of 2.6 2.5 etc etc...

again, any ideas on how to solve this issue???

Thanks

ok, first it's not an issue.

When you tested Ze, You disconnected the earthing conductor which went to the earth rod I imagine.

As previosuly mentioned, you may well have bonding in place to the Water service???

Try testing with the earthing conductor re-connected, and you will probibly get a reading of somewhere around 2 ohms. As previsouly stated by telerix, by connecting the water pipe you've effectivly got a much better earth rod!

With regards to the values in the Regs - Being a TT system, because your Ze is not garenteed stable, circuits must be protected via RCD (in your case 30ma), which from what you say they already are.
 
Last edited by a moderator:
ZE was 187

the system is protected by a 30ma RCD from the main house, and the new board is also protected by a 30 ma RCD.

would that be a 30mA RCD protecting the sub main and another 30mA RCD protecting the final circuits in the outbuilding i.e. 2 RCD's in series

I was too slow in replying to specialist (too slow, specialist beat me) sorry to cause confusion
 
Last edited:
I'm busy writing an FAQ on TT systems for a certain organisation, judging by some of the questions (and answers) on this thread, I need to write faster!
 

Reply to Very Hi ZS Reading on TT system? any advice in the Australia area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi All Let me start by saying I have my 2365 level 3 but never worked in the industry so my knowledge is limited. My partner and I recently...
Replies
22
Views
2K
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K
Hi.... First time I've posted here. I own a property which is rented out. Recently the Gas Oven failed a gas safety test and the Gas Engineers...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock