Gentlemen
I have a question for your perusal. A 3kW 230volt submersible pump is connected to a long extension cable (60 metres). Approximate current drawn is I=3000watts/230volts = 13amps (ignoring PF and efficiency). Cable is rated at 0.03 volts/amp/metre therefore the volt drop is 0.03x13x60 = 23volts.
If the current drawn is recalculated subtracting the voltage dropped we have: I=3000/207 =14.5A
So if the pump continued to do 3KW’s worth of work it would now require 14.5amps due to the voltage dropped by the cable.
My question is this: would this happen in reality or would the added resistance of the cable just reduce the current to the pump?
Thank you for your attention.
I have a question for your perusal. A 3kW 230volt submersible pump is connected to a long extension cable (60 metres). Approximate current drawn is I=3000watts/230volts = 13amps (ignoring PF and efficiency). Cable is rated at 0.03 volts/amp/metre therefore the volt drop is 0.03x13x60 = 23volts.
If the current drawn is recalculated subtracting the voltage dropped we have: I=3000/207 =14.5A
So if the pump continued to do 3KW’s worth of work it would now require 14.5amps due to the voltage dropped by the cable.
My question is this: would this happen in reality or would the added resistance of the cable just reduce the current to the pump?