compmad1

Hi, I want solar pv panels: a 4KW system. My roof is large and south facing, but shadow is cast by a rather large chimney.

Solar Edge power optimizers have been recommended by one company, but a different company has reservations about fitting this system because of the expense of scaffolding required if an optimizer needed to be replaced.

Even though the power optimizers have a 25 year manufacturers warranty, apparently Solar Edge are not confident enough about the reliability of their system to enable them to cover labour expenses etc.

I'd appreciate others opinions on Solar Edge power optimizers, and advice on any other effective solutions to the problem of shading.

My brother-in-law was not advised correctly about his new system --- lots of shade and panels connected in series. His system was not generating much electricity at all. His company are supposed to be fitting individual inverters on each panel now, but I don't know much about this.

I did not know anything about solar panels until a week ago, and would appreciate any advice at all. Thanks.
 
We have had problems with two optimisers out of around 3-4k , solar edge paid us to change it. Depends on the relationship you have with your manufacturer, ours is pretty strong with solar edge.
 
Solar edge systems are great, very well made, I've installed quite a few of them and I've never had a problem, the company are very helpful and I wouldn't think you'd have any problems with warranty. The monitoring system is also good, very informative, They're very good for maximum generation at different points of the day with various shading issues.. There is an evecsys system with uses an inverter for each panel. I personally prefer the solar edge system.
 
Any chance of some pictures? (maybe screenshot captures from google maps)

The shading might not be as bad as you fear and there are lots of clever tricks which could be used to get the best from the panels even if they suffer hard shadow at certain times of day.
 
We actually visited the OP this morning and discussed the options and we recommended that they post on this forum to get some impartial advice.

I'll design the system on PV Sol Expert tomorrow morning and post the layout on here. I personally don't think a Solar Edge system is required but won't know until I've tried a couple of designs.

It is interesting that Wersolar says that Solar Edge paid him to change the optimisers as this hasn't been our previous experience. Although a conversation I had earlier in the week with someone from the company suggests that this situation may change. To be honest, I think it is the very least that a company should do to back up their product.

Even with this back up, I am not convinced that Solar Edge would be the best option with the extra expense involved. It will be interesting to see what other installers' opinions are.
 
I have made this clear with them that they need to make it more clear in there warranty statement, I said this was major negative point, they have a great USP in there product. I think you can't expect a full scaffold rig being paid for but a small donation maybe a benefit in the form of 100-200 pounds, we didn't receive a great deal other than two free optimisers but that was enough for me.
 
We like Solar Edge but tend to use it only when installing on three or more roof surfaces, not because of shading issues.

The online monitoring system is good once set up. It's great to be able to analyse each panel individually.

We haven't yet had a problem with Solar Edge so haven't needed to test their after-sales or warranty service.
 
Depends on the shading, but we'd usually use an SMA or Power One dual string inverter with full scan shading function, which works to use the panels bypass diodes to cut out the shaded cells and avoid the system getting stuck on a false peak.

The important thing to make this work is to design the system properly to ensure the shadow comes across the panels to maximise the use of the bypass diodes - ie not running across the short side.

It works pretty well, and saves around £1k vs microinverters / solar edge - takes a hell of a long time to make back that £1k from the 2-5% or so performance advantage I'd expect from microinverters vs the performance from these specific inverters if set up correctly.

Also worth bearing in mind that microinverters will only cut out one shaded string within the panel, if 2 out of 3 strings are shaded then it will function at the output of the shaded cells, so it doesn't actually deal with shading that well within the shaded panels, just prevents the shading from impacting on other panels.
 
Enphase, 20 year warranty. they will change the inverter for you or pay you to do it. 24hr / 7 day monitoring, and alert status to the installer if one of the panels fails. Could improve performance by 12% versus string inverter. More money piece of mind for 20 years. Also low voltage DC on roof rather then 250v DC plus. Just a thought.
 
Okay, below are a couple of screenshots of our PV*Sol model for this project.

The roof faces just 10degrees off south and the two shading issues come from the chimney and the neighbouring property to the south.
Screenshot_Screenshot1.jpgScreenshot_Screenshot2.jpg

I've placed some REC 260w panels in this design and laid them in the least shaded areas.

Screenshot_Screenshot3.jpg The chimney clearly gives the most shading but with the panels in this layout, most of the shading is cast on the lower row of panels.

Screenshot_Screenshot4.jpg This screenshot shows the shade cast on 13th October at 3pm.

I've tried a few different string configurations and I get a yield of 3,542kWh on a Power One 3.6. With a Solar Edge system, I get a yield of 3,627kWh.

The yield loss due to shading on the Power One option comes in at 6.9% and at 6% on the SolarEdge system. The extra yield on the Solar Edge system probably comes from the increased yield as mismatch penalties don't apply.

I would think that it would be a judgement call. Personally I am not a big fan of having too much electronic equipment on a roof and I would argue it should be avoided if possible. In this instance I would say that the shading cast on the roof doesn't warrant a SE system.

It'd be interesting to know others' thoughts.
 
Any chance of some pictures? (maybe screenshot captures from google maps)

The shading might not be as bad as you fear and there are lots of clever tricks which could be used to get the best from the panels even if they suffer hard shadow at certain times of day.

Thanks for your help. I have attached a picture of our house from Google Earth. It is the house with the word 'Peveril' running across the front of it. Looking at the picture I have noticed some other shading as well, presumably from the house in front.
 

Attachments

  • roof.JPG
    27 KB · Views: 30
I have made this clear with them that they need to make it more clear in there warranty statement, I said this was major negative point, they have a great USP in there product. I think you can't expect a full scaffold rig being paid for but a small donation maybe a benefit in the form of 100-200 pounds, we didn't receive a great deal other than two free optimisers but that was enough for me.

If Solar Edge are so confident that their product is reliable, why don't they back their product with a FULL guarantee with the cost of scaffold and labour included? Why should an installer carry the cost of replacing someone else's product?
 
It'd be interesting to know others' thoughts.

Is it viable to have all the panels arranged in landscape as close to the ridge and/or as far to the right as possible? I reckon the roof is wide enough to take rows of six along the ridge and at least four per row on the unshaded right. The sun would have to be very low in the sky to affect those on the ridgeline.
 
Is it viable to have all the panels arranged in landscape as close to the ridge and/or as far to the right as possible? I reckon the roof is wide enough to take rows of six along the ridge and at least four per row on the unshaded right. The sun would have to be very low in the sky to affect those on the ridgeline.

Can only get 5 in a row in landscape and the layout receives more shading this way.
 
I'd stick with that layout then.

I would worry about an "upper" and a "lower" string because in autumn, winter and spring that chimney is going to play games with the leftmost five panels on the upper row.

If we number the panels 1-15, starting at the top left as #1, the top right as #9 and with #10 being the one on the bottom row closest the chimney, I think I'd have the eight on the right (6,7,8,9,12,13,14,15) on one MPPT and the seven on the left (1,2,3,4,5,11,12) on another.
I appreciate that #5 has less impairment than #12 and you might want the least-impaired panels on one string, but I think in the afternoons #5 will be more affected than #12 as the sun shines between the chimney and the neighbour's roof (your first image shows what I mean).

The second string is going to be a bit of a mess and rarely reach its full potential, but a scan function for optimum voltage should be able to keep it running close to three-quarters potential on sunny days (and no noticeable losses on the many cloudy days).
 
Actually, I think you'd be surprised. Which is why PV Sol is such an excellent piece of software.

You can try different string set ups and it will recommend a best option. No guess work. I've been trying to post a video to show you what I mean.
 
As I said before - Power-One probably split into 8 and 7, set the full MPPT scan function to 5 minutes, and maybe adjust the low voltage setting down to allow for lower string voltages on the shaded side when shading has knocked out a few of the strings within the panels.

string systems underperform badly in shaded conditions when the installer doesn't know what they're doing, and either spec an unsuitable inverter, or don't set it up properly.

As your numbers indicate, solar edge would likely outperform the power-one, but not really by enough to justify the extra expense in this situation IMO.
 
Actually, I think you'd be surprised. Which is why PV Sol is such an excellent piece of software.

You can try different string set ups and it will recommend a best option. No guess work. I've been trying to post a video to show you what I mean.

My concern - and reason for suggesting a left/right split - is there are two different causes of shading, and the shading is at different times of day.
The left-most panels are affected by the chimney in the afternoons and evenings at any time of year.
The lower row of panels are affected by the neighbour's roof around mid-day in winter.

I worry that mixing left and right might end up with a complex mix of shading almost all day. But by splitting off the right-most eight panels they benefit from no shade at any time of day during spring, summer and autumn (when about 90% of annual generation occurs).

But as already said by others: two strings and getting the inverter to scan the voltage should keep losses to manageable levels. However you configure it I would expect it to meet the SAP-2009 estimate for a 3.7-4kWp array that isn't shaded.
 
Last edited by a moderator:
This video shows the shade cast on the roof over a year. It's a long watch but an interesting one.

[video=youtube;49dUf4sYIus]http://www.youtube.com/watch?v=49dUf4sYIus[/video]

It's worth nothing how the shade cast by the chimney affects the array at different times of the year. Shade cast in the winter if far less of a worry than shade cast in summer and you'll notice that the chimney tends to affect the lower row of panels only in the summer months.
 
What is the best way to overcome the problem of shade from a chimney?


Knock it down???

come on geordie. knock it down is a plumber's solution. as electricians we would carefully demolish it brick by brick, stacking said bricks neatly in the garden for the client to make a water feature from it, being careful not to shade his PV array.
 
Any chance of some pictures? (maybe screenshot captures from google maps)

The shading might not be as bad as you fear and there are lots of clever tricks which could be used to get the best from the panels even if they suffer hard shadow at certain times of day.

Thanks. I did upload a picture from Google Earth, but being new to the forum, I don't think I am allowed to at the moment. Solar City have put up some good pictures with the PV Sol Expert software. Thanks for all the advice you are giving.
 
Ah, it faces SSE which makes the neighbour's roof shadow on the lower panels worse than expected.

I still wonder if landscape layout (two rows of five or six in landscape close to the apex) - or at least exploring its possibilities with the software - would help the upper row's bypass diodes gradually adjust the panel output so that maybe even without voltage scanning the loss of just one-third of a panel could be sufficiently close to the optimum voltage that the inverter would find it or not be far from it even if tracking a false peak.
The chimney knocking out one-third of a panel in a string of eight is only going to change the voltage going through that string by 10V (out of 240V) which won't be far from the optimum of the curve.
 
No, it faces just 10 degrees off south towards west.

Ah, you set the view from the West, rather than the convention for maps which is South!

Looking at the video I wonder whether the changing shade conditions (and the angle from which the shade comes) are sufficiently gradual that a single string of fifteen panels might work surprisingly well because the panels will be affected one-by-one and by only 2% as each bypass section drops out (giving time for the MPPT to adjust).

In summary: I think the shading looks worse than it actually will be in the real world. It will be a nuisance but probably not enough to affect the array's ability to reach its SAP target except in really cloudy summers when we all will struggle! I think sensible design and a quality inverter would deal with most of the problems. I wouldn't be over-keen on micro-inverters because of the hassle if they go wrong (especially if the company behind the warranty is no longer trading at some point in the future).
 
@SolarCity, just watched the video..
I would normally have chosen a string inverter (Power One or SMA both with their shading options switched on) configured with the heaviest shaded panels in a single string, configured similar to how FB suggested.
However this summer we did some playing around with string inverters and Solar edge and noticed that at certain times of day the string inverters where up to 30% down on power compared to the SE when we had shading similar to that from the neighbour's roof, i.e only covered a part of the bottom of the panel. - We were actually staggered at the result and so double checked it.

SE is a far better solution than micro-inverters in most cases - See my comments in a previous string about start up voltages on micro-inverters. However you still have to weigh up the extra cost of the Solar Edge over the potentially improved output..
 
Last edited:
The extra yield predicted isn't that great. I can imagine at certain times the increase may be 30% for a short amount of time but the modelling doesn't suggest that this would make much difference over the year.
 
The 30% wasn't across the whole day. It happened to be during the peak sunny periods in the summer (remember that :) ) when we did the experiments, and we were only measuring instantaneous power, not total energy for the day..
 
I had a very similar problem to this when my system was installed and received a lot of help from this forum the thread is here http://www.electriciansforums.co.uk...ergy-forum/53090-correct-inverter-choice.html

Here is a picture of my shading.

Chimney.jpg

In addition to the chimney I have shading of the bottom panels during winter from nearby trees.

You would have to read the thread to get all the details but the system performed very badly and we changed to SolarEdge.

I have been very pleased with the SolarEdge system. For me it seems to have been a very good solution. The extra cost was not that significant (this was installed when a 4Kw system cost 10-12K) You can also factor in the monitoring which is something you might might have to pay for with other systems.

What the monitoring does prove is how much is lost per panel due to shade, see image below which shows total output per panel since installation.

Panels.jpg

This shows that there is not much loss due to the shade with SE installed, before the loss was huge albeit on a poorly installed system.

The only downside for me has been trying to deal with SE as a consumer. They really don't want to deal with consumers and for this reason getting the monitoring setup was a nightmare. I still don't have full access so I am unable to update the tariff changes when they happen which is really disappointing. If you do go down the SE route make sure your installer is willing to register your system and update tariffs in the future because you cannot do this easily yourself.

Hope the above is useful.
 
come on geordie. knock it down is a plumber's solution. as electricians we would carefully demolish it brick by brick, stacking said bricks neatly in the garden for the client to make a water feature from it, being careful not to shade his PV array.

Sorry Tel ... I wasn't thinking - must have been a "Senior Moment".
 
I would strongly recommend people research manufacturers financial situation a certain microinverter company aren't posting great profits compared to solar edge who seem to have it cracked. Enphase and solar edge are made in the same factory in china so quality is there on both products, as for bypass diodes conducting on micros it has a great effect and can totally knock out the inverter making it useless in shading conditions, but as for solar edge it works on a fixed string voltage and is not reliant on min voltages coming for panels the optimiser and inverter work together to adjust the voltage on the panel to optimal output, Dc to dc optimisation is the way for my company and it does not cost 1k extra to install either around 600
 
Good thread. Very educational and great contributions from many sources. A couple of thoughts:

1) Have you considered reducing to 14 panels and increasing wattage on each? You could get rid of that 6.7% stinker. Maybe go for Yingli 275s x 14 = 3.85kWp. Combined with the Power One 3.6, this might work ok. Or even BenQ 325s x 12 = 3.90kWp and kick out 3 weak performers.

2) Have you considered going over 4kWp and installing on the opposite roof surface? You could cover both sides and go for G59 or maybe just a few on the other side and stick with G83. Yes, it would increase the overall cost, but it might reduce the pence per watt/peak figure. It could be a real goer with an Immersun-type device. The FiT level isn’t that much lower for the 4kWp-10kWp band these days (13.50p v 14.90p).
 
I had a very similar problem to this when my system was installed and received a lot of help from this forum the thread is here http://www.electriciansforums.co.uk...ergy-forum/53090-correct-inverter-choice.html

Here is a picture of my shading.

View attachment 20971

In addition to the chimney I have shading of the bottom panels during winter from nearby trees.

You would have to read the thread to get all the details but the system performed very badly and we changed to SolarEdge.

I have been very pleased with the SolarEdge system. For me it seems to have been a very good solution. The extra cost was not that significant (this was installed when a 4Kw system cost 10-12K) You can also factor in the monitoring which is something you might might have to pay for with other systems.

What the monitoring does prove is how much is lost per panel due to shade, see image below which shows total output per panel since installation.

View attachment 20972

This shows that there is not much loss due to the shade with SE installed, before the loss was huge albeit on a poorly installed system.

The only downside for me has been trying to deal with SE as a consumer. They really don't want to deal with consumers and for this reason getting the monitoring setup was a nightmare. I still don't have full access so I am unable to update the tariff changes when they happen which is really disappointing. If you do go down the SE route make sure your installer is willing to register your system and update tariffs in the future because you cannot do this easily yourself.

Hope the above is useful.

Thanks for the info. In what way was yours a poorly installed system?
 
Thanks for the info. In what way was yours a poorly installed system?

It was a rush job to beat the FIT tariff drop deadline in December 2011.

Fitted on two strings the voltage was not high enough for the inverter. The inverter was not a good choice where you have shade, there are much better choices such as SMA and Power One.

The standard of roof work and internal cabling was poor although this was partially rectified when the installers revisited to install the SolarEdge.

My best advice would be take your time, do your research and preferably use a contributor from this forum for the install. It looks like you are doing all three so will probably get it right.

Hope that helps.
 

Reply to What is the best way to overcome the problem of shade from a chimney? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
945
Hey guys, hoping someone can help with my problem.! A client of mine asked me to rig-up a little solar system to power a diaphragm air pump...
Replies
2
Views
1K
Good Morning All! Always appreciate reading the great ideas and conversations in the forums, and now actually have a chance to ask a question...
Replies
0
Views
897
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I have an electric car and an air source heat pump (so we use quite a bit of electricity). We have a house with south-facing roof. I've had a few...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top