Hi,

Should a burglar alarm be wired directly onto the consumer unit or is it acceptable to hard wire it onto an existing socket?

Thanks,

Jon
 
Hi,

Is it OK for the Alarm panel, which is in an adjoining garage, (to the kitchen) to be spurred off a socket in the kitchen or should it have been spurred off from a supply in the garage, (which is on its own circuit)

Jon
 
Hi,

Should a burglar alarm be wired directly onto the consumer unit or is it acceptable to hard wire it onto an existing socket?

Thanks,

Jon

Never direct into a consumer unit.

Always through an unswitched fused spur, preferably fed direct from the consumer unit on a 6A MCB.

Spur should be fused at 3A.
 
Hi,

Is it OK for the Alarm panel, which is in an adjoining garage, (to the kitchen) to be spurred off a socket in the kitchen or should it have been spurred off from a supply in the garage, (which is on its own circuit)

Jon
Spur can be fed from kitchen but should be adjacent to the control panel (within 2m) Likely need to cable spur in 4mm T&E.
 

Reply to Wiring of Burglar Alarms in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi All, Please may I ask if light fixtures must now always be fitted by an electrician? also for domestic homes, is it okay for there to be a...
Replies
4
Views
784
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
317
Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
703
Hello all I hope you are well. I had a new Alarm Panel installed in January and all was working well until I got a new Consumer Unit installed...
Replies
18
Views
2K
Hi all, I currently have a Pyronix Enforcer V10 Wireless alarm system. I have some shock/contacts on windows, doors, PIRs, and an external siren...
Replies
0
Views
763

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock