I'm not sure how to handle the other possible issues you have mentioned.
The REC should advise when replacing the distribution board, as we are required by RECI and the CRU to ensure that the tails are adequate (16mm^2 is the minimum permitted by the ESB - if you have old 6mm^2 tails for example then they will have to be replaced), that the main equipotential bonding conductors are sized correctly (minimum 10mm^2) with a minimum 10mm^2 Earthing conductor to the Earth electrode. Your main protective conductor (neutralising link) will, if not 10mm^2 be replaced with a 16mm^2 conductor - this would typically have been 10mm^2 before the T&E was replaced in 2017.

But your REC should advise on all of this.

If you don't have an isolator or meter with an inbuilt isolator and contractor's seal (realistically it's unlikely that you will for the age of the installation) then you will need to log a job with the ESB and pay them for the tails to be upgraded. The REC will provide a Cert No. 1 to this end.
 
Industrial type fuse I think. Can't remember the proper name.
It's a Diazed fuse.

Some of these were withdrawn as they were shown to be a fire hazard. They were replaced with Neozed fuses. Now MCBs and RCBOs are the norm, although a switch fuse could still be used for the main overcurrent device where the tails are less than 3 metres in total. Otherwise an MCB with a minimum short circuit current rating of 9kA (which realistically means a 10kA device minimum as no 9kA devices exist) must be fitted in an IP rated enclosure in the Permalli Box.
 
The REC should advise when replacing the distribution board, as we are required by RECI and the CRU to ensure that the tails are adequate (16mm^2 is the minimum permitted by the ESB - if you have old 6mm^2 tails for example then they will have to be replaced), that the main equipotential bonding conductors are sized correctly (minimum 10mm^2) with a minimum 10mm^2 Earthing conductor to the Earth electrode. Your main protective conductor (neutralising link) will, if not 10mm^2 be replaced with a 16mm^2 conductor - this would typically have been 10mm^2 before the T&E was replaced in 2017.

But your REC should advise on all of this.

If you don't have an isolator or meter with an inbuilt isolator and contractor's seal (realistically it's unlikely that you will for the age of the installation) then you will need to log a job with the ESB and pay them for the tails to be upgraded. The REC will provide a Cert No. 1 to this end.


Great! Thank you for such extended advice!
 

Reply to Workers accidentally cut the wire... I'm looking for advice. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
339
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
910
I removed my baseboard electrical heaters (1981 installed) due to finishing off the room. When I had a new AC ductwork installed they changed the...
Replies
2
Views
422
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hello, I would liked to install a Byron wired doorbell with built in chime and 8v transformer. I'm struggling to get power source. I have a...
Replies
1
Views
462

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock