I have got a job to do in a local hairdresser to change a consumer unit fed off an economy 7 meter.

My question is do you need to test and notify the works like you would in a domestic dwelling? Also is it mandatory that the incoming services of water/gas are bonded with 10mm earth.

I know this is the correct procedure for domestic installs but this is our first non domestic job and we want to get it right.
Thanks
 
10mm bonding is the correct procedure for domestic installs? First I heard of it.

Have you been living under a rock?

Of course if you use the adiabatic equation you could probably get away with 6mm but any good electrician will always use 10mm the cost difference is minimal.
 
The sizes for main protective bonding conductors are mentioned in reg 544.1. Size would depend on the supply and size of earthing conductor and/or neutral conductor.

I expect most domestic properties with a PME supply, it would be 10mm, but not necessarily. I guess that's what Hightower refers to.

Scope of Part P, is refered to in that document 1.3.2.(citation my green OSG). I think, I might be wrong, but the adiabetic question formula is used to calculate protective conductors.
 
  • Like
Reactions: westward10
Have you been living under a rock?

Of course if you use the adiabatic equation you could probably get away with 6mm but any good electrician will always use 10mm the cost difference is minimal.

I'd argue the opposite, in that any good electrician will always figure out if 10mm is needed rather than just upgrading it for the sake of it. Okay, the cable may not cost much, but some bonding runs are a nightmare. From the calculations I've done over the past few years I've yet to encounter a house with a TT or TN-S supply that actually needs 10mm.
 
Agree with hightower. See if it is needed, especially if it's a complicated run. Daz.
 
  • Like
Reactions: Dave OCD
I thought the 'adiabatic is used for sizing of the earth conductor and protective conductors, not bonding conductors.
Bonding conductor sizes are selected from the calculated (or selected using tables) size of earth conductor or protective conductor'??
 
I'd argue the opposite, in that any good electrician will always figure out if 10mm is needed rather than just upgrading it for the sake of it. Okay, the cable may not cost much, but some bonding runs are a nightmare. From the calculations I've done over the past few years I've yet to encounter a house with a TT or TN-S supply that actually needs 10mm.
What calculations are these.
OP, have you checked for bonding yet.
 
Doh. Main bonding not main earthing conductor. Must read question properly. Or rtfq . Daz.
 
For myself, domestic work, I find it simpler to have a drum of 10mm in the van to use for bonding services. I've even used it for earthing conductor for TT :)
 
What calculations are these.

The adiabatic to size the earthing conductor, then bonding conductors can be sized based on the result of this.

For myself, domestic work, I find it simpler to have a drum of 10mm in the van to use for bonding services. I've even used it for earthing conductor for TT :)

That's what we have - massive roll of 10mm, and it gets lashed in for everything. But the OP said it was procedure to have 10mm in domestic for bonding when this simply isn't true.
 
Think that's the problem with being a bit aloof with ones replies, people get the wrong end of the stick and a little bit excited.

OP, you still there?
 
The adiabatic to size the earthing conductor, then bonding conductors can be sized based on the result of this.
I find it difficult to believe anyone would do this on a rudimentary domestic installation.



That's what we have - massive roll of 10mm, and it gets lashed in for everything. But the OP said it was procedure to have 10mm in domestic for bonding when this simply isn't true.
 
Far as I know you can't touch economy 7 electrics. And anyway what possible use would it be to a business unless they operate at night? Must be missing something.
 
Many small shops have storage heating, why can't you touch it.
 
10mm2 is the minimum CSA for both earth and bonding conductors where PME conditions apply.
Where PME conditions do not apply, the minimum CSA for earth conductors is determined by use of the adiabatic equation, for bonding conductors it is 6mm2.
Of course you can touch Economy 7 electrics.
 
Yes and you shouldn't get a shock during normal working hours unless the meter's dodgy. :D
 
As far as i know the work is not notifiable as it is not domestic, just issue an ecr for the work you carry out and keep a copy for your records
 
As far as i know the work is not notifiable as it is not domestic, just issue an ecr for the work you carry out and keep a copy for your records
That's not quite correct, I think, if you read Scope Part P (#6).
 
  • Like
Reactions: Flanders
That's not quite correct, I think, if you read Scope Part P (#6).
Yes thought the op was talking about a self contained unit but as you say if its a shared meter with a flat above or at the back then its notifiable
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Does it need it?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
Liam howe,
Last reply from
sparksburnout,
Replies
23
Views
2,952

Advert