Discuss Fault on underground Sub Mains cable in the UK Electrical Forum area at ElectriciansForums.net
Hi,
I am currently in the middle of completing a new installation in time for a Halloween event at a local activity centre. Over the weekend, while I was not there, it seems that they have lost power to the sub mains distribution panel.
Unfortunately I didn't have my Megger to hand yesterday as it is being calibrated, I will get it back later today, so I couldn't test the cable.
I have 400V across all three phases and neutral at the Sub station end, protected by 3 x 300A BS88 fuses. The 120mm 4Core SWA is buried direct in to the ground and runs 530m. At the other end it is connected in to a PowerPact panel. I have no voltage at the panel end. The fuse chamber was still in the on position at the sub station, but upon testing to see if I have voltage at the distribution panel end I only have continuity beep between all three phases and neutral.
I did notice that L1 fuse has blown, which I replaced yesterday but still no voltage.
I feel that the cable must be damaged underground, but I don't see how it can stay on at the fuse chamber? Any ideas?
I will be able to test the cable later today.
Also if it is damaged underground, does any one know of any tester out there to find the section of damaged cable, as its a 530m run and digging that back up will be costly!!
Yes I will be testing the cable later once I get my Megger back from the wholesalers. if the cable is damaged, which it must be, I can;t see why the fuse chamber stays ON and doesn't blow?
A bit of enthusiastic back filling is a likely culprit . What kind of spoil was the dig?
If you google 'Cat and Genny' you will get a load of specialists that do this , or you can hire the gear yourself.
Its quarry stone, backfield with a layer of sand the quarry stone. I didn't see the backfill myself, but that was over a month ago now. The cable past all tests then, IR, R1+R2, Zs, PFC, PSCC etc.
Hi,
Quarry stone will do it every time especially if there is activity on the made up ground.
Our cable crossing frequently gave as a firework display.
Good chance a sharp rock has travelled down and pierced the cable, the backfill will have been loose and settled , the rest with a bit of help from the traffic.
Obviously I will be able to tell later when I complete R1+R2 and IR tests
But it will still stay in the On position, do you think clean cut? Because I should have a least have 1 or 2 phases if partly damaged?
Had the same fault as above but on a smaller scale (only 30m-35m run).
BS88 L1 blowing taking out a third of a small office block. No obvious reason why until I looked at the newly laid cable run. It was across the entrance of a private car park and the entrance was being used for access to a new building site next door. An empty excavation truck went over the new tarmac and nothing happened. 5 minuets later a loaded truck drove over it and BANG!
Dug up the trench and they may have well used sharpen granite for back fill! It had a "dusting" of sand and the rest was just big chunks of rock. Narrow down your search, hire one of the testers above and check wherever a road goes over the cable run.
Any sand bed under and over the cable, or cable tiles covering the cable, or has it just been chucked in Willy Nilly and back filled with whatever spoil was left from digging the trench?
I know sand bed under and over of 100mm I was there for that, as I know they wouldn't if I didn't make that clear. Back filled with excavated spoil, I understand
As already mentioned then possible high traffic area might be the site of the fault, you could hire those testers I posted info on, but it's a specialist operation, best bet maybe would be to get a cable tracing company in, the one I used way back was THOMAS CLARKE, don't know if they are still in existence, but a quick google search would come up with option. Good Luck.
If you can access it you can trace it. However if there are areas that are difficult to access, but you know the route accurately, you could TDR it to find out how far away the fault is from 0ne end. With a reasonable fix from that, a likely cause such as recent groundworks may present itself near the expected fault position.
Sorry whats TDR?
Rough calc volt drop would be about 20v for 120mm For that length at 300amp using x value
Is nobody else thisnking this??
Sorry we probably should for mixed loads, In that case its even worse?
Yes I'm thinking the same, and in my opinion you are correct.
But in the interests of 'being nice' I'm staying quiet so far.
In the interests of 'being nice' also i'll say no more....
function gen a oscilloscope, look for the reflection, do the maths and bingo you'll know where the cable break is(good Luck)
long sds bit. drill down along the run. when the sds bit stops going bang, you've found the break. :eek::eek:
Reply to Fault on underground Sub Mains cable in the UK Electrical Forum area at ElectriciansForums.net
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
4K
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
