What lamps are in these fittings?
What type of rcbo is it B,C.
Have you tried disconnecting the photocell and switching through a standard switch?
Reactions: static zap
we will have to wait for the post mortem
I'm afraid.
Clamp the circuit to see what the current draw is.
( Daft thought do check contactor is
switching Live , not the other one !)
....Heat steams things up then ....
I would like to know If the rcbo is actually required.
It's a type b rcbo, more good ideas, many heads better than one on this one.
Staring at a cct in the cold today was probably not a good idea, the street lamp heads on due to swap tomorrow might be getting kicked into touch at this rate too!
I would still like to know if the rcbo is required.
Not according to BS7671.
However it is a requirement of BS7671, not to leave the installation less safe.
Why would it be less safe if an alternative device provides fault protection. If it is a TN system and installation methods permit an rcd may not be required for additional protection and would be compliant with BS7671.
It’s not a matter of compliance, it’s a matter of safety.
Is a circuit more safe because it has RCD protection, no safer or less safe?
Maybe the contactor is disconnecting the live and neutral slightly out of sink,one is opening before the other causing a momentary imbalance that the Rcbo sees as a earth fault
Reactions: Wilko
If a non rcd protective device provides overcurrent and fault protection without the need for additional rcd protection it is fully compliant.