S

s18mcn

Hello, ive just been to look at a job where the main fuse is in the middle of the kitchen due to an extension. The owner wants to tidy it up and move the fuseboard to other side of the doo, and the main head back outside. Would it be ok to run a 16mm t+e sub feed from the new metre position fe dvia a 63A breker to the new board with a seperate 10mm earth wire?
Also the board thats their is a split load one but due to the moving of it to its new position it has to be upgraded to 17th edition right?
 
Hello, ive just been to look at a job where the main fuse is in the middle of the kitchen due to an extension. The owner wants to tidy it up and move the fuseboard to other side of the doo, and the main head back outside. Would it be ok to run a 16mm t+e sub feed from the new metre position fe dvia a 63A breker to the new board with a seperate 10mm earth wire?
Also the board thats their is a split load one but due to the moving of it to its new position it has to be upgraded to 17th edition right?

You could use 16mm however, you may need to RCD protect it, which would then go against regs, depends on your chosen installation method.

No need to change CU, just use RCBO's where needed.
 
You could use 16mm however, you may need to RCD protect it, which would then go against regs, depends on your chosen installation method.

No need to change CU, just use RCBO's where needed.

Why would this be against regs? Discrimination?
 
This is very odd, I have just come on line to ask exactly the same questions with the same sinareo! I was going to take the 16mm t + E from garager to new board from a 60 a switch fuse but was also wondering about rcd as I wasn't sure about 2 in parrelel
 
use swa ( no rcd required ) to feed new ccu then fit your dual rcd board as normal .fitting two 30ma rcds in line is a big no no !!! discrimination will not take place!! depending on the sensitivity of the rcd ( if you was to use one ) protecting the feed to the new ccu this could trip could trip before the one in the new ccu causing you to loose all your circuits in the new ccu

Rich
 
Ive also seen a job where a 63A breaker has been installed next to metre then a 16mm t+e run to consumer unit. Is this also bad practice??
 
Chaps.

I know its hot but you need to have a little think :D

Will the submain need 30 mA RCD protection??
 
Ive also seen a job where a 63A breaker has been installed next to metre then a 16mm t+e run to consumer unit. Is this also bad practice??

I hate to say it but thats what iv done in the past, only due to the fact that I have been told to. I was in no position to argue it as I knew no better being a 2nd year apprentice. I just assumed that the 60a Isolator is the protective device if the T+E is damaged.

.fitting two 30ma rcds in line is a big no no !!!
So in a new dual RCD board. 100amp Main SW. and 2x30a RCDS is a no no?
 
.


So in a new dual RCD board. 100amp Main SW. and 2x30a RCDS is a no no?

What you are trying to achieve with those RCD's is to stop the whole CU going off should a fault on one circuit appear.

Thats why 2 RCD's protect 2 "sets" of circuits.

If you install an RCD ahead of the submain due to installation methods, this will not comply as, in effect, one RCD is covering the whole installation which is not permitted.

Make sense?:D
 
What you are trying to achieve with those RCD's is to stop the whole CU going off should a fault on one circuit appear.

Thats why 2 RCD's protect 2 "sets" of circuits.

If you install an RCD ahead of the submain due to installation methods, this will not comply as, in effect, one RCD is covering the whole installation which is not permitted.

Make sense?:D

Yeah iv got that, so you wouldn't install an RCD at the meter that would be a DP isolator? :o
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
mains change
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
s18mcn,
Last reply from
Spudnik,
Replies
12
Views
2,229

Advert