Hi All,

I would like to have a Ring Video Doorbell fitted to my garage - the version 2 which runs directly off the hard wired doorbell.

The Issue

I don't have a doorbell at present and the garage Consumer Unit (see pic) is full. I have been provided with the following advice;

Solution 1 (The costly one)
Have a larger CU installed and have a Wylex Bell transformer attached to the Din Rail so that the bell wire runs directly to the Ring device.

Solution 2 (The budget one)
Add a separate feed to the existing lighting MCB and then to a wall mounted bell transformer and onwards to the Ring device.

My questions are:

1. Is there an advantage to having a bell transformer within the CU ?

2. The 16amp MCB (wall sockets and door opener) in the CU already has two separate feeds into it as there wasn't enough room in the box when the electrician originally fitted them, so I'm presuming (NEVER PRESUME !!) that 'doubling up' would be ok for the 6amp lighting MCB ?

3. Is there a Third solution (without opting for a wireless Ring Device) ?

Many thanks in advance for your thoughts.

Paul
 

Attachments

  • Garage CU .JPG
    Garage CU .JPG
    371.2 KB · Views: 52
Yes, another 2 module enclosure next to the one in your picture that will contain the doorbell transformer. Fed directly from the lighting MCB.
 
tap into the lighting MCB and fit a stand alone transformer.
 
  • Like
Reactions: i=p/u
The transformer doesn’t have to go at the CU.... fused outlet off the socket circuit, or tapped off at a light switch (if you have live and neutral)

I can’t believe the transformer that comes with Ring has exposed terminals
 
  • Like
Reactions: Paul N and loz2754
So we can put a ring transformer in a Cu, but not an mcb from a different manufacturer of the CU???

mans we need 2, 3 spare ways?
 
Yes. Any DIN standard device can be fitted into any DIN rail consumer unit, as it is not fitted to the bus bar.
But you might have to cut the busbar to make it fit.... isn’t that altering original parts?

im not trying to disagree with anything here.... just devils advocate.
 
But you might have to cut the busbar to make it fit.... isn’t that altering original parts?

im not trying to disagree with anything here.... just devils advocate.
Cutting a bus bar is something you have to do in many consumer units anyway.
 
tap into the lighting MCB and fit a stand alone transformer.
Hi Telectrix,

Thank you for your advice - very helpful.

Regards,

Paul
 
  • Like
Reactions: loz2754
Cutting a bus bar is something you have to do in many consumer units anyway.
Hi there,

Thank you for taking the time to explain about the DIN rail transformers I hadn't thought about checking them for being standardised fits, this would save a lot as the prices are very different between Wylex and e.g. BG. Thanks once again Paul
 
  • Like
Reactions: loz2754

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Doncaster
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Third Solution Anyone ?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Paul N,
Last reply from
Paul N,
Replies
11
Views
1,753

Advert