Hi guys,

When installing a new CU does anyone ever install a 100A double pole isolator switch between the meter and the consumer unit?

Very often I come across 16mm tails which need to be upgraded to 25mm so I join the old tails to new in a Henley block and get the DNO to come and upgrade their side at their convenience.

Instead of using a henley block could I use an isolator instead?

In anyones opinion would there be any disadvantages to this?

I wouldhave thought having an isolator would be very handy but the meter guys hardly ever bother putting one in, even now.

They're also relatively inexpensive. Another thing, I cannot seem to finda 2-module metal enclosure so would this would be okay in a plastic enclosure? That to me seems like a bit of grey area.

Any help appreciated. Thanks
 
The meter installers will never put one in as this will increase cost.

And yes it does make sense to fit an isolator, especially as a lot of smart meters will detect when the fuse has been pulled and may not allow the power to come back on.

Plenty of switches out there to choose from: Wylex 100A DP Supply Isolator - https://www.tlc-direct.co.uk/Products/WYREC2S.html?source=adwords&ad_position=1o1&ad_id=45425533757&placement=&kw=&network=g&matchtype=&ad_type=pla&product_id=WYREC2S&product_partition_id=174057653827&test=finalurl_v2&gclid=CjwKCAiA-KzSBRAnEiwAkmQ157Kt_x523muqnFlf4y4TXEAW-EshYmwvjADqoV6nxokuHPGgm8Vz1hoCdV0QAvD_BwE
 
Generally the only time 25mm tails are a must In domestic are new builds where the local DNO requests 25mm tails and a 16mm earthing conductor as standard ,usually because a 100amp fuse has been fitted.
 
Metal or plastic. I've asked for my scheme technical a few times now as to whether such an isolator needs to comply with reg 421.1.201, and the response has been somewhat vague.

In fairness it would perhaps be more clear cut, where such an isolator would be installed in a domestic property. Not perhaps in an outside mounted meter box, but they would not give definitive answer. It would be down to 'the designer to risk access'. When the 18th draft was up for comment, I did suggest a better definition than 'similar switchgear'. Something to consider perhaps?
 
Metal or plastic. I've asked for my scheme technical a few times now as to whether such an isolator needs to comply with reg 421.1.201, and the response has been somewhat vague.

In fairness it would perhaps be more clear cut, where such an isolator would be installed in a domestic property. Not perhaps in an outside mounted meter box, but they would not give definitive answer. It would be down to 'the designer to risk access'. When the 18th draft was up for comment, I did suggest a better definition than 'similar switchgear'. Something to consider perhaps?

I've seen enough official guidance to convince me that a DP isolator does not fall under the wording or intent of that reg.
 
I haven't, can you share?

Similar switchgear assemblies
The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:

Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’

Consumer units - IET Electrical - http://electrical.------.org/wiring-matters/55/consumer-units/index.cfm
 
Similar switchgear assemblies
The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:

Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’

Consumer units - IET Electrical - http://electrical.------.org/wiring-matters/55/consumer-units/index.cfm

421.1.201 refers to consumer units and similar switchgear. In BS7671 Switchgear is defined as 'an assembly of main & auxiliary switching equipment for operation, regulation, protection or other control of an electrical installation'. That's sounds like an isolator to me?
 
Forgetting about whoever installs it then, IF an isolator can be fitted that is of a plastic nature, surely then, that answers all of our questions?
 
421.1.201 refers to consumer units and similar switchgear. In BS7671 Switchgear is defined as 'an assembly of main & auxiliary switching equipment for operation, regulation, protection or other control of an electrical installation'. That's sounds like an isolator to me?

Yep an isolator would fall under the definition of switchgear, but the IET guidance on the matter clearly says that similar switchgear refers to switchgear similar to a CU in function. It's poorly written in my opinion though.
 
Forgetting about whoever installs it then, IF an isolator can be fitted that is of a plastic nature, surely then, that answers all of our questions?

Systems for the distribution of electricity to the public, is excluded from the scope of BS7671, reg 110.2 (i). So if the DNO/Supply fit an isolator, it does not need to comply with BS7671, as far as I'm aware.
 
Just to show I'm not trying to be argumentative, here's my question and answer I received from Certsure technical (I've even left in the spelling mistake);

1. Sometimes the installation of meter tails to a new consumer have to protected by a switch fuse. Would the use of Wylex plastic switch fuse, REC 2 or similar plastic isolators, being installed in an external plastic meter box on an external wall, be defined as being installed ‘within domestic premises’?


'The Suppliers and meter equipment would fall outside the scope of BS7671.
As a designer installing any equipment in external meter enclosures we would suggest a risk assessment is carried out to make a judgment of the likelihood that fire originating inside the enclosure or similar switchgear might lead to the outbreak of fire in the household building. We trust this answers your questions'.
 
'The Suppliers and meter equipment would fall outside the scope of BS7671.
As a designer installing any equipment in external meter enclosures we would suggest a risk assessment is carried out to make a judgment of the likelihood that fire originating inside the enclosure or similar switchgear might lead to the outbreak of fire in the household building. We trust this answers your questions'.
So basically they haven't got a clue and just pass the blame onto you... :D
 
So what they are saying is, if you choose to install an isolator you should carry out a risk assessment to cover your own --- in case it catches on fire through fault or negligence. That is what it sounds like to me...?
 
that wylex unit has a 16mm earth terminal why does it not have a 25mm terminal,when normally you would be using 25mm swa in it ?.fitted one last week real pain for the earth
 
that wylex unit has a 16mm earth terminal why does it not have a 25mm terminal,when normally you would be using 25mm swa in it ?.fitted one last week real pain for the earth
Why would you use a 25mm earthing conductor in domestic?
25mm 2 core swa or 16mm for the line and neutral and a separate 16mm earthing conductor ran in parallel surely?
 
So what they are saying is, if you choose to install an isolator you should carry out a risk assessment to cover your own --- in case it catches on fire through fault or negligence. That is what it sounds like to me...?

IMO I can rarely see the time when 'I' would install an isolator. I can see the occasion when I would install a switch fuse isolator, in which case I would install a metal one.

However, the other consideration is, would the DNO/Supplier allow you to fit a metal enclosure in 'their' meter cabinet?
 
Why would you use a 25mm earthing conductor in domestic?
25mm 2 core swa or 16mm for the line and neutral and a separate 16mm earthing conductor ran in parallel surely?

I probably go for a 25mm 3c myself, mostly if it weren't too long. Installing one thing instead of two things. But then I'm lazy.
 
IMO I can rarely see the time when 'I' would install an isolator. I can see the occasion when I would install a switch fuse isolator, in which case I would install a metal one.

However, the other consideration is, would the DNO/Supplier allow you to fit a metal enclosure in 'their' meter cabinet?
To be honest I can’t see you fitting one in their meter box as you just don’t have the room.
It’s hard work trying to convince a builder to fit a 2nd meter box to house the fused isolator
 
To be honest I can’t see you fitting one in their meter box as you just don’t have the room.
It’s hard work trying to convince a builder to fit a 2nd meter box to house the fused isolator

I did come close to fitting one in a cabinet on one job. Was room just. Got to the point of enquiring with the DNO, but when I measured my tails run, it was 3m. :D
 
I did come close to fitting one in a cabinet on one job. Was room just. Got to the point of enquiring with the DNO, but when I measured my tails run, it was 3m. :D
My experience regarding the length of the ‘tails’ with the DNO is basically “we don’t care”
 
Murdoch, does it not specify in BS7671 that all supplies must now be 25mm regardless?

No - but the "pretty" pictures in the OSG do suggest this is the case.

When I do a CU change I carry 25mm tails, 16mm GY and 10mm GY and the appropriate Henley blocks and MET's - then I can cover each eventuality....

If its a new build I certainly would fit 25mm tails.
 
421.1.201 as everyone knows requires the enclosures of CUs and similar switchgear to be made from a non-flammable material (essentially metal).
However 421.1.201 also requires that they comply with BS EN 61439-3, which most everyone seems to forget.

So if your DP 100A isolator or switchfuse does not comply with BS EN 61439-3, you cannot install it irrespective of whether the enclosure is metal or even if you enclose it within a metal cabinate or enclosure.

Unfortunately, BS EN 61439-3 only applies to CUs, so you won’t be able to install either a DP 100A isolator or switchfuse.
 
Should point out, that the previous post only applies if you believe DP 100A isolators and switchfuses are similar to CUs.
If you don’t believe they are similar, then you can still install them and they can be plastic, metal or whatever.

I believe I'm paying too much tax to HRMC. I'm arguing, they are not believing.
 

Reply to 100A DP Isolator Installation Between Meter and CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Hi, need your advise please as need to take supply for Electric car charger from the meter cupboard. This meter cupboard has an isolator and...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock