HI..
I'm in Scotland, UK..
The 15a Wylex push button breaker that supplies my garage with power (30m from the house mains panel) randomly trips.
I threw the isolator switch in the garage, so there was nothing loading the circuit but it still trips out after a few hours.
Changed the breaker to see if it was developing a hair trigger, but to no avail.
I disconnected the cable at the panel and also at the garage's isolator and measured the resistance values in ohms between the E, L & N at each end of the supply cable which are:
House..
E-L 11K, E-N 10K, L-N 5K
Garage..
E-L 5K, E-N 1K, L-N 3K
Could anyone tell me what these values should be for the 30m cable supply to my garage before I retreat to the 1m crawl space underneath my house and start tracing it out (no idea where the cable routes under my back garden, but I can probably trace it under the house).
Cheers.
 
When you tested the cable, was it totally disconnected from everything? The mcb, the neutral and earth bar?

What did you use to test? Just a multimeter won’t be accurate enough.

The cable, with nothing connected either end should have insulation resistance values in the Mega Ohm scale, not kilo ohm

Could it be rodent damage to the cable? Any other signs of the little critters?



Those push button circuit breakers are getting old now… and it might be worth your while having the consumer unit changed…. Which will introduce all the new equipment needed to satisfy the regulations including RCDs and an SPD.
 
@littlespark is spot on with the fact that although a multimeter won't give you an accurate picture of the condition of the cable, the readings are on the order of a thousand times too low. We probably don't need an actual insulation tester to tell us there's damage somewhere. The readings you give won't in themselves trip an MCB, but they hint at the kind of fault that will arc over or break down under mains voltage.

What type of cable is it? Do you know whether there are joints?
 

Reply to 15a breaker randomly tripping.. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I want to verify if the breaker size is correct for the service going into my detached garage. I have 6 AWG cable going from my main panel in my...
Replies
0
Views
974
Hi everyone. I have a basement that was finished years ago. The basement is on a separate panel than the rest of the house. For years I've had...
Replies
2
Views
1K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
708
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
625
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock