Evening all

Guy who owns a small industrial unit currently has 100amp 3phase

At the moment he only have a single phase baord with feeds a few lights and sockets. He wants to install a 20a 3phase supply for a something

The mem 20a 3phase switch fuse i got only allows upto 16mm tails and not 25mm. Would using 16mm tails be ok for 100amp supply? The power being drawn wont exceed 20amp so i cant see the issue
 
I would be most surprised if 16mm conductors fit a MEM switch fuse.
 
Regardless of whether or not the tails will fit in the switch fuse it is fine as the 20A fuses will provide upstream protection of the tails. In theory you could use any tails rated above 20A.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
16mm tails on 3phase
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
TJC1,
Last reply from
Sintra,
Replies
2
Views
1,357

Advert