soulman
Hi, i require a little advice. 3 phase supply (100A per phase) from energy meter into 3 phase switched fuse isolator, then swa off to D.B 20 metres away. Distribution board feeds office equipment only. I need to install a supply for a 36kw 3p machine, which is going to be situated next to intake. My question is, can i tap into the switched fuse isolator, provided i can get my cable in. Then swa to 63A switched fuse to supply machine. I have spoken to 2 sparks & both have gave me different answers.
Any help appreciated.
Instead of tapping into the isolator can you not make off into Henley blocks then to your switched fuse? Providing maximum demand throughout is ok.
Reactions: 1 person
Really depends what your max demand is on the overall installation (I'm assuming 36kW isn't a typo). If your 100A intake can handle the extra load then yes, although I wouldn't be tapping directly in to the switch fuse, I'd go into a little busbar chamber if I could, worst case scenario if cost is an issue and you can be sure of no more similar additions then tap into a few henley blocks in a nice enclosure.
Edit: beaten to it!
Reactions: 2 people
Thanks guys, that's really helpful. This is not my usual sort of work. Max demand is o.k just office equipment, no real loads. I like the idea of henleys in an enclosure. I shall also check out a small busbar chamber.
Out of curiosity what are the two solutions the other sparks gave? If they were conflicting.
3 phase advice
soulman,
Scornio,