Hi, I have been tasked with installing 3 phase ring main in a tool room. X6 16A sockets. Each pice if kit will pull no more than 5A. Planning on using 4mm SWA cable protected by a 63A breaker. Tool room dimensions are 7M X 5M. Any problems with this?
 
Hi, I have been tasked with installing 3 phase ring main in a tool room. X6 16A sockets. Each pice if kit will pull no more than 5A. Planning on using 4mm SWA cable protected by a 63A breaker. Tool room dimensions are 7M X 5M. Any problems with this?
How many cores in the 4mm2
 
Will this circuit be a a final circuit or a Distribution Ring? I see phasing problems, not the sort of circuit I would install. If it was my choice I would use some sort of Busbar 3 phase trunking and drop down to each outlet that requires power, using the appropriate trunking adaptors that are suitable for a W/Shop environment.
 
Last edited:
I think you need to reconsider your design, 16A sockets on a 63A protective device. As a ring final circuit, why?
 
It seems an odd thing to do but assuming each socket has additional rcd protection and is correctly designed with regard to vd and current carrying capacity it would be difficult to say it is incorrect, non-conventional maybe. BS7671 only references 30/32A ring final circuits whereby live conductors should not be less than 0.67 of the protective device so whether you can apply this I couldn't say for certain.
 
63A breaker isn't set in stone, was just thinking about the cable rating. Drill pulls less than 5A and the rest of the kit even less. Be rare more than 2 buts of kit will ever run at the same time. I am utilising gear we already have
 
I know a couple of companies that still have 200A rings round the units.
 
Thanks for the help, not my normal job role, was concerned about over looking something. Same tool room is to also have a 240 ring X6 16A sockets and a single 32A radial for a welder
 
In practice it will be 100% fine, although it does seem a bit over-engineered for the present usage. Would run on two 20A radials, no local MCBs needed, and still have room for more.
 
I'd be looking at using 20 amp OCPD either ring or radial. Bear in mind that the devices will have no overload protection for the flexes.
 

Reply to 3 phase ring main in a tool room. X6 16A sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
986
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock