How many cores in the 4mm2Hi, I have been tasked with installing 3 phase ring main in a tool room. X6 16A sockets. Each pice if kit will pull no more than 5A. Planning on using 4mm SWA cable protected by a 63A breaker. Tool room dimensions are 7M X 5M. Any problems with this?
Will this circuit be a a final circuit or a Distribution Ring? I see phasing problems, not the sort of circuit I would install. If it was my choice I would use some sort of Busbar 3 phase trunking and drop down to each outlet that requires power, using the appropriate trunking adaptors that are suitable for a W/Shop environment.4 core