just wondering what other people think of wiring leg out to a ring in a single swa 4core 2.5 using the armoring as the earth?
its about 10 mtrs from the board and wouldnt have massive loading on the end.
i know that using 2 seperate pieces is best but i have a piece of 4 core long enough and am thinking bout using it .
 
be sure to gland and fly lead it if you're using the armour as cpc.
 
you may laugh, but seen that done several times.
 
Just a little cautionary thought - your L or N ring will be 20m long ring but your armour only 10m assuming you are having a 32amp front end then your csa of the armour may not be sufficient enough to ensure you meet your ELI requirements as you have effectively taken half the earth ring away and left a radial earth.
 
he said "may not be sufficient". time to do some calculations.
 
4 core SWA amour = 20mm² whereas the minimum requirement is 5.7mm² (single circuit) for steel wire.

Where’s the problem if the SWA is terminated properly?
 
4 core SWA amour = 20mm² whereas the minimum requirement is 5.7mm² (single circuit) for steel wire.

Where’s the problem if the SWA is terminated properly?

Spoiling my fun Tony ;)- trying to get him to think like an Electrician if he checked it he'd realise it was well within tolerances with spare.. but being told yes its ok won't get him to realise why its ok... but as he never counted my post with yes it works out fine i assume he didn't bother checking.

Ive stopped giving out straight answers now im getting the OP's to contribute to solving their issues more and understand the calcs behind it as it seems less and less now bother with them as scary as it sounds.
 

Reply to 4 core swa feeding ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
425
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!! I am planning a...
Replies
13
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock