Discuss 4 core swa feeding ring in the UK Electrical Forum area at ElectriciansForums.net
just wondering what other people think of wiring leg out to a ring in a single swa 4core 2.5 using the armoring as the earth?
its about 10 mtrs from the board and wouldnt have massive loading on the end.
i know that using 2 seperate pieces is best but i have a piece of 4 core long enough and am thinking bout using it .
be sure to gland and fly lead it if you're using the armour as cpc.
you may laugh, but seen that done several times.
Just a little cautionary thought - your L or N ring will be 20m long ring but your armour only 10m assuming you are having a 32amp front end then your csa of the armour may not be sufficient enough to ensure you meet your ELI requirements as you have effectively taken half the earth ring away and left a radial earth.
he said "may not be sufficient". time to do some calculations.
4 core SWA amour = 20mm² whereas the minimum requirement is 5.7mm² (single circuit) for steel wire.
Where’s the problem if the SWA is terminated properly?
Spoiling my fun Tony ;)- trying to get him to think like an Electrician if he checked it he'd realise it was well within tolerances with spare.. but being told yes its ok won't get him to realise why its ok... but as he never counted my post with yes it works out fine i assume he didn't bother checking.
Ive stopped giving out straight answers now im getting the OP's to contribute to solving their issues more and understand the calcs behind it as it seems less and less now bother with them as scary as it sounds.