shane

HELLO This is my first post on here and i have a daft question .I have a125amp 3 phase 4 wire 415v/50hz supply from a diesel gennerator 105kva.the customer wants 12- 600watt discharge lights installing with a timer to do the switching,i've done all the cable, powerfactor and discrimination calcs and i have desided to wire them in 2.5mm2 swa to an adaptable box then from the box to the lights in 1.5mm2 not swa,,in 3 rows of 4 using and a bank of 3-2 module contactors ct no(2 POLE 230V) and a timer to do switching.i have 3- 2 module merlin gerin ct no 20 amp in the van here and now,
can i mount them straight in the 3 phase distribution board or should i get a modular enclosure and feed them from a 3 phase type c breaker in the distribution board.
any advice and comments please are welcomed.:)
 
Last edited by a moderator:
600w discharge lighting :S:S seen 400w n 1000w not seen 600w that aside Personaly id split the 12 across the 3 phases and wire using 6mm swa to box then 2.5mm to the fitting
 
yeh i was gonna split over 3 phases mate .. i'm in middle of nowhere and this guys wanta them doing asap, thats only kit i have in van. i did the calcs quick and came to 23 amps over 3 phases thats why i thought 2.5mm2... cheers any way
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
600 watt discharge lighting and contactors
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
shane,
Last reply from
shane,
Replies
3
Views
2,193

Advert