morning guys
What do you guys normally do for a swa supply down to a garden office- where the customer doesnt want the swa viewable inside- so swa needs to be made off outside and then cores coming into the back of the consumer unit.
I know I could use a ip65 plastic box as I have fly banjo'ed at house end- but I like doing it either end
I know wiska do the banjo things for plastic wiska boxes- but don't think they do a 25mm one do they? (cable is 3core 10mm)
and the normally galv adapt boxes are not ip rated are they?
I know some people use the galv and just stick a gasket in there
what are your methods??
cheers