hillbillie

How do you do an earth bond test for these? I have re read the IEE code of practice on this but I can't find an answer apart form: "...can give misleading results"

For example a class 1, totally plastic vacuum cleaner, at least on the outside (it has tiny metal screws not screwed into earthed metal). If there is nowhere to stick your lead can it be tested? Should I just do a visual and the insulation resistance test?
 
There's sometimes a little hole where you can poke your probe :D.
The 'by the book' answer would be to contact the manufacturer to find out how it's supposed to be tested, but personally I would just do the other inspections and tests.
 
Also think about AC adaptors or power supplies, some of which have no earth connected - even at ther output terminal - yet are constructed and fed with a dedicated IEC power cord.
In this case the earthed power cord is used to provide an earth for the correct fuctioning of the internal electronics and not to provide a CPC.

In this instance Adaptor is tested as Class II and power cord separately as IEC (extenion lead) and a note made to that effect.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
class 1 equipment with no exposed earthed metal
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
hillbillie,
Last reply from
Patman,
Replies
2
Views
6,839

Advert