Afternoon all,

I need to switch a reasonably high load (higher than 13 amps) on an several electric underfloor heating circuits. I'm assuming I can use a contactor for this.

Having never wired one before, I thought I'd just double check the connections:

A1/A2 - Wire the normal feed to the underfloor matting from the stat to these contacts on the contactor?
1/2 - Wire live through these?
3/4 - Wire neutral through these?

Many thanks

Euan
 
A1 and A2 are the connections to the coil of the contactor so assuming its a 230v coil then you put a neutral to A2 and switch return from stat to A1. The rest of what you said is fine. Make sure stat and coil are fused correctly.
 
prob 1 pole per circuit

AC1 rating will prob do -doubt there's any significant 'inrush'


if it's just switching via contactor i'd normally be switching line/phases only through contacts(assuming separate local isolation)

you can measure the 'cold resistance' of the elements and compare it to the rated wattage of the elements if you're interested in that sort of thing:D
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Contactors
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
2

Thread Tags

Tags Tags
contactors

Advert

Thread statistics

Created
EWebster,
Last reply from
davelerave,
Replies
2
Views
4,717

Advert