Hello
I am currently rewiring an old house which has tails in basement from meter going into a 60A fused isolator which feeds all the existing circuits from a fusebox in an inconvenient location, to be made redundant.
I need to send power to both a consumer unit in the basement, and a separate CU on the ground floor which will feed circuits at ground level and upstairs level.
DO I:
Treat Ground Floor CU as a sub main, therefore run SWA/ other from Basement to upstairs ? The cable I intend to run above the plasterboard ceiling, poss fixed to the joists
OR
Go from isolator straight to GF CU and send back to basement using that as the 'sub'? The basement may be let to tenants therefore upstairs inhabitants may prefer if possible not to have their CU running off a breaker in the basement.
OR
Feed both CUs independently from the isolator switch/ fix up a 2nd isolator switches?
What is the better option?
Then- can I up the fuse rating in this isolator switch? I'm concerned that the maximum demand may exceed 60A if it was upstream of both CUs.
Anyone got any ideas?
Many thanks,
Nick
Hi Lee
I'm not self-cert yet, just practical experience and some C&G qualifications in testing & inspecting, 17th edition and Part P. The LABC have been contacted.
one more 60a isolator, link it up to that henley block and use swa for cable run upstairs.
existing one use for a separate consumer unit in the basement.
Hello
DO I:
OR
OR
Many thanks,
Nick
If there's any possibility of the basement being let to tenants, I'd use the existing switch fuse to supply the ground floor board and install a board for the basement run direct off the Henley block (provided it's within 3m).
Dependent on assessment of load, of course.
You then have the option of easily metering the basement supply or putting it on its own DNO supply at a later date.
Not separate property- basement to be used as granny annexe/ spare guest accommodation.
So what's this then??
If this is the case, then the installation will need to accommodate the needs of both tenant and the homeowner. That means provision for a second meter among other things!!
I've a feeling this is your first rewire after a short course at a training center, and it's not as straight forward as you thought!!
If the basement is going to be let out to tenants then the main house's meter will ideally want moving into the house.
A seperate supply for the basement shouldn't be too hard considering there is a TP head there, then it prevents any hassle with splitting the electricity bill.
i would feed the upstairs board from the isolator provided and henley block into a small 2 way fuseboard for the basement. Then you could run swa of this one to the basement fuseboard position. Just a thought
Reply to Cu in basement and separate cu upstairs ground floor? in the UK Electrical Forum area at ElectriciansForums.net
I have an existing EmerGen Switch installed in my main panel that links to 10 breakers. The main panel is located in the basement. I recently...
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...