diditrain

~
Arms
Jul 30, 2008
670
195
101,218
north west
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
I am trying to find a replacement programmable thermostat to retrofit onto an existing installation, as the existing one has got a blank screen. Batteries have been replaced and various buttons/reset has been tried to no avail.

The original one is now obsolete. Can anyone recommend one that may be suitable?
The supply to the controller is 24 volt when measured between terminals 1 and 2 there is also a remote sensor installed.
Don’t really want to start messing about with the wiring, if I can help it as there are more of the same controllers in the same installation, serving other rooms.
 

Attachments

  • IMG_2446.jpeg
    IMG_2446.jpeg
    335.9 KB · Views: 14
I am trying to find a replacement programmable thermostat to retrofit onto an existing installation, as the existing one has got a blank screen. Batteries have been replaced and various buttons/reset has been tried to no avail.

The original one is now obsolete. Can anyone recommend one that may be suitable?
The supply to the controller is 24 volt when measured between terminals 1 and 2 there is also a remote sensor installed.
Don’t really want to start messing about with the wiring, if I can help it as there are more of the same controllers in the same installation, serving other rooms.
I am trying to find a replacement programmable thermostat to retrofit onto an existing installation, as the existing one has got a blank screen. Batteries have been replaced and various buttons/reset has been tried to no avail.

The original one is now obsolete. Can anyone recommend one that may be suitable?
The supply to the controller is 24 volt when measured between terminals 1 and 2 there is also a remote sensor installed.
Don’t really want to start messing about with the wiring, if I can help it as there are more of the same controllers in the same installation, serving other rooms.
some other photos of controller hopefully
https://Upload the image directly to the thread.com/rFwEtpU
https://Upload the image directly to the thread.com/rnBKImS
 
Looks like a single channel switch will do, just on off for theboiler. Suggest Danfoss TPone and RX1 receiver (screwfix do them) Get the RF version so no wiring. I am not sure if you have that already. If you have, sure the batteries aint dead? Or if mains supplied then is there a supply?
 
Last edited:
Looks like a single channel switch will do, just on off for theboiler. Suggest Danfoss TPone and RX1 receiver (screwfix do them) Get the RF version so no wiring. I am not sure if you have that already. If you have, sure the batteries aint dead? Or if mains supplied then is there a supply?
Cheers: will look into them.
 
Cheers: will look into them.
The TPOne-B is a direct replacement for what you have.
The terminals 1 and 2 are the relay contacts for 'heat'. The 24V you measured between them is not a supply voltage (the unit is battery powered), but an artifact of what's on the other end of that circuit.

I feel you don't really need the rf version as the wires are already there and have been doing the job for the last 10+ years!
 
The TPOne-B is a direct replacement for what you have.
The terminals 1 and 2 are the relay contacts for 'heat'. The 24V you measured between them is not a supply voltage (the unit is battery powered), but an artifact of what's on the other end of that circuit.

I feel you don't really need the rf version as the wires are already there and have been doing the job for the last 10+ years!
That seems to make a bit more sense. There are various relays and valves at the other end, as you say. You didn’t install it by any chance did you?
 
That seems to make a bit more sense. There are various relays and valves at the other end, as you say. You didn’t install it by any chance did you?
😂 No. If only! I've just dealt with a few different thermostats and programmers since my first in about 1970 🤪
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

diditrain

Arms
~
Joined
Location
north west
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Danfoss programmable stat replacement
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
10

Thread Tags

Advert

Thread statistics

Created
diditrain,
Last reply from
Avo Mk8,
Replies
10
Views
2,097

Advert