sue1955

Hello,

I have my house on the market and have recently had a fullreferb. The house hasn’t been rewired but my electricain removed the trunkingthat was all around the house and chased the cables into the walls and put newswitches, lights and sockets etc.

The house did have smoke detectors hardwired but theplasters boarded the complete house and didn’t pull the cables down so I had toinstall battery ones.

A buyer has just had her electrician inspect the house andhe has picked up the following isssue, my electrician is on holiday for 2 weeksand I need to know if I have to get these points fixed or if the electricianwho inspected in wrong?



I have twofuseboards, the one with the bathroom lights on is RCBO C6 and the other boardhas two RCD’s and circuit 1 doesn’t have a fuse in it??? Please help???

Defects:

· Absenceof RCD protection for cables installed at a depth of less than 50 mm from asurface of a wall or partition where the cables do not incorporate an earthedmetallic covering, are not enclosed in earthed metalwork, or are notmechanically protected against penetration by nails and the like – C3

Covered in thebelow consumer upgrade

· Absenceof 30ma RCD protection for circuits supplying equipment in a locationcontaining a bath or shower with insufficient supplementary bonding - lights up– C2

Replace theexisting consumer unit to a split load RCD protection and new circuitprotection

· Smokedetector on ground floor past expiration date – FI

Replace smokedetector to main linked type

· Absenceof smoke detector on 1st floor – FI
Supply and install1no smoke detector

· Absenceof smoke detector in loft conversion – FI

Supply and install1no smoke detection

· Absenceof heat detector in kitchen – FI
Supply and install1no heat detector
· Circuit1 has no identification –C3
Identify circuit or make safe.

 

Attachments

  • 20140629_144110.jpg
    20140629_144110.jpg
    198 KB · Views: 16
  • 20140629_144121.jpg
    20140629_144121.jpg
    201.4 KB · Views: 14
From the information you have supplied and assuming that the consumer unit pictures you have posted are the only ones in the property.

All your circuits have 30mA RCD protection so any reference to lack of RCD protection is incorrect.

If your circuits are installed correctly and you have main bonding to incoming metallic services then supplementary bonding is not required in a bathroom.

The reference to circuit one appears to indicate there is a connected circuit, however this would be very unlikely since that positions a blank.
All the circuits pictured have identification so this appears to be an inaccurate observation.

The lack of, or expiry of smoke alarms and the absence of mains powered smoke alarms is for information only.
However it would be in general a good idea to have in date mains powered smoke alarms in the property.
 
  • Like
Reactions: 1 person
he's either fishing for work, or the prospective buyer is trying to get the price knocked down.
 
  • Like
Reactions: 1 person
sounds like a made up code 1 (fire).
 
I assumed FI was "For Information" since it relates to smoke alarms that are not covered by an EICR.
 
  • Like
Reactions: 1 person
comments? what's wrong with just entering " it's FUBAR"
 
Maybe the guy who inspected doesn't know what an RCBO is.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Electrical Safety Inspection?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
sue1955,
Last reply from
aesmith,
Replies
9
Views
1,765

Advert