1. 2.5mm T+E on radial, 20A breaker feeding 1 FCU that feeds water heater, can I come off this FCU with another FCU to feed a heater?

2. 2.5mm ring main, consisting off FCU and sockets all on ring, can I come off one of these FCU to feed a FCU spur?
 
Thanks was just unsure of 2nd question so I’ll have in and out of fused connection and another to new fused connection unit?

You would have to come in and out of the first FCU or you could otherwise have 2 or more FCUs with 13amp fuses that would exceed the current carrying capacity of the 2.5mm t/e spur. You could always have the first FCU non switched and onto the next FCU (switched or non switched) where you don't have to come in and out or that would defeat the point of a second or more FCU if it was only powered if the first FCU was switched on.

I know some might suggest that if for instance you had 3 FCUs on a ring spur and they all had 3 amp fuses in this would be acceptable, but anyone could change the fuses to 13amps so I wouldn't do it this way (no big deal fitting a 13 amp non switched FCU where you come off the ring).
 

Reply to Fused connection unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I found a 13A FCU, connected to the kitchen ring supplying an outdoor junction box, providing two SWA 2.5mm radials. Unconventional? yes. One...
Replies
2
Views
800
Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Replies
9
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
618
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
736
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock