So how do you feel about running in a suitably sized separate CPC that can take care of both the bonding and circuit protective conductor in the event of your DNO supply being PME'ed?? In the meantime it can be used as a link to an additional earth rod position at the garage via the garage EMT back to the MET in the house, and providing a suitable means of bonding to the extraneous water pipe in the garage. The TT rods can be left connected to the MET/EMT if and when a PME connection has been made available....


As davesparks has suggested, the existing Ra can be significantly improved from 14 ohms with a little thought and effort. Plus the lower the Ra achieved, will make all the difference if and when a PME earth is provided by the DNO, not to mention the existing TT system....
 
So how do you feel about running in a suitably sized separate CPC that can take care of both the bonding and circuit protective conductor in the event of your DNO supply being PME'ed?? In the meantime it can be used as a link to an additional earth rod position at the garage via the garage EMT back to the MET in the house, and providing a suitable means of bonding to the extraneous water pipe in the garage. The TT rods can be left connected to the MET/EMT if and when a PME connection has been made available....


As davesparks has suggested, the existing Ra can be significantly improved from 14 ohms with a little thought and effort. Plus the lower the Ra achieved, will make all the difference if and when a PME earth is provided by the DNO, not to mention the existing TT system....
It's definitely doable. That's a good call actually, the house next door to me was converted to PME when they had the cutout moved during a kitchen extension and they are fed from the same string of overhead lines. That was two years ago.
 
Right now we have established it is a separate electrical installation, I would follow Dave and E54s advice , also as I said in post #17
"my gut feeling would have been to make my sub-main 6mm 3 core, as it is TT, or possibly even 10mm in case they ever update it to PME, especially if it is buried."

I speak from experience here :) lol as this happened to me a few years ago lol, luckily we had ducted the SWA cable, the DNO had updated the OH supply to ABC cabling and converted everyone in that area from TT to PME, they sent letters to every householder warning of the need to get their bonding checked, we had only laid the sub-main about 7 month previously.

Now I consider that the price difference of 10mm to 6mm SWA to be negligible on domestic installs compared to the cost of upheaval of replacing unless it is very simple to do.

Edit: and run a local MPB from the incoming water pipe (in the garage) to the garage CU EMET.
 
Last edited:

Reply to Garage Metalwork in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
470
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi My main feed comes into the garage, feeds into the meter and then out to another box with a 60AMP fuse then into the house...
Replies
20
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock