Hello sparkies
I have stopped by because i have a slight problem in my house.
I am a master plumber, I have worked with you guys for years,
I hope you would be so kind as to steer me in the right direction.
when my AC kicks on, my lights blink.
From what I know, that aint good.
I have a 200 amp service so that is not the problem
any guesses as to wth is up?

stuffed.jpg
 
Hello sparkies
I have stopped by because i have a slight problem in my house.
I am a master plumber, I have worked with you guys for years,
I hope you would be so kind as to steer me in the right direction.
when my AC kicks on, my lights blink.
From what I know, that aint good.
I have a 200 amp service so that is not the problem
any guesses as to wth is up?

View attachment 52120
If I have to guess
Hello sparkies
I have stopped by because i have a slight problem in my house.
I am a master plumber, I have worked with you guys for years,
I hope you would be so kind as to steer me in the right direction.
when my AC kicks on, my lights blink.
From what I know, that aint good.
I have a 200 amp service so that is not the problem
any guesses as to wth is up?

View attachment 52120
Hello sparkies
I have stopped by because i have a slight problem in my house.
I am a master plumber, I have worked with you guys for years,
I hope you would be so kind as to steer me in the right direction.
when my AC kicks on, my lights blink.
From what I know, that aint good.
I have a 200 amp service so that is not the problem
any guesses as to wth is up?

View attachment 52120
If I had to guess I would say there is a loose connection, I don’t what size unit you
Ok..I will check the breaker box. tighten up the connections and report back tomorrow around the same time

thanks man.
frod you be careful and turn off breakers while checking
 
Hello sparkies
I have stopped by because i have a slight problem in my house.
I am a master plumber, I have worked with you guys for years,
I hope you would be so kind as to steer me in the right direction.
when my AC kicks on, my lights blink.
From what I know, that aint good.
I have a 200 amp service so that is not the problem
any guesses as to wth is up?

View attachment 52120
Is the wiring to the A.C sized correcrly? sounds like you may have a Volt drop problem in your House
 
yes sir, it is a big --- orange wire. 10/3 if i remember correctly the unit is a 3 ton unit
" A big --- Orange Wire 10/3" can't seem to find that a cable of that description in the Regs Book!!! Don't think many Electricians over in the UK will be familiar with it either.
 
What size motor is on your AC and how is it controlled IE powered direct (DOL) to bring it on instantly or speed controlled to ramp it up?... it is not unusual for the inrush of a motor DOL to cause local flickering although we do have regulation over here about this and adding transients to the network which may effect other uses.

It is quite possible your local distribution Network feeding your property is already heavily loaded thus making the inrush of your A/C show up annoying side effect, if this is the case there are options to suppress this but not really cheap.

This is all assuming the previous suggestions of a loose common point in the system is not the cause.
 
What size motor is on your AC and how is it controlled IE powered direct (DOL) to bring it on instantly or speed controlled to ramp it up?... it is not unusual for the inrush of a motor DOL to cause local flickering although we do have regulation over here about this and adding transients to the network which may effect other uses.

It is quite possible your local distribution Network feeding your property is already heavily loaded thus making the inrush of your A/C show up annoying side effect, if this is the case there are options to suppress this but not really cheap.

This is all assuming the previous suggestions of a loose common point in the system is not the cause.
Frodo have you check your connections yet. I have a 3 ton unit myself and my lights don’t flickers it’s not a big load. I suspect that your problem is in your main panel
[automerge]1568371901[/automerge]
" A big --- Orange Wire 10/3" can't seem to find that a cable of that description in the Regs Book!!! Don't think many Electricians over in the UK will be familiar with it either.
How are doing today Pete
 
Last edited:
YES I did. I jut checked it a few minutes ago. a loose connection on the breaker screw

Thanks guys. I hate freaking wires
30 years ago, I was laying under a kitchen sink {new Construction} hooking it up and the wire to the disposal zapped my ear . I jumped up and chased that damn sparky all over the house and into the yard. we became good friends after that
 
YES I did. I jut checked it a few minutes ago. a loose connection on the breaker screw

Thanks guys. I hate freaking wires
30 years ago, I was laying under a kitchen sink {new Construction} hooking it up and the wire to the disposal zapped my ear . I jumped up and chased that damn sparky all over the house and into the yard. we became good friends after that
Have you turned the air conditioning on yet to verify it’s fixed
 
Frodo have you check your connections yet. I have a 3 ton unit myself and my lights don’t flickers it’s not a big load. I suspect that your problem is in your main panel
[automerge]1568371901[/automerge]

How are doing today Pete
Oh so so, thanks for asking.
[automerge]1568378593[/automerge]
Have you turned the air conditioning on yet to verify it’s fixed
Glad you fixed it, not a loose Fire Nut then?:):D:cool:
 
YES I did. I jut checked it a few minutes ago. a loose connection on the breaker screw

Thanks guys. I hate freaking wires
30 years ago, I was laying under a kitchen sink {new Construction} hooking it up and the wire to the disposal zapped my ear . I jumped up and chased that damn sparky all over the house and into the yard. we became good friends after that

That's why we do thorough testing over here!
 
That's why we do thorough testing over here!
DPG are you saying that we don’t do no kind of testing. We are not that reckless and if I wire something or do service calls I guarantee you that I know without a doubt there will be no problems. I know what I’m doing do you
[automerge]1568382086[/automerge]
DPG are you saying that we don’t do no kind of testing. We are not that reckless and if I wire something or do service calls I guarantee you that I know without a doubt there will be no problems. I know what I’m doing do you
I have been doing electrical work for 32 years and don’t insult my intelligence, we do have our share of dumb asses just like y’all
 
DPG are you saying that we don’t do no kind of testing. We are not that reckless and if I wire something or do service calls I guarantee you that I know without a doubt there will be no problems. I know what I’m doing do you
[automerge]1568382086[/automerge]

I have been doing electrical work for 32 years and don’t insult my intelligence, we do have our share of dumb asses just like y’all
Yeah we certainly have our fair share Mw, although and I'm not including your good self, most of the YOUTUBE VIDS of US electricians, don't appear to have any test instruments in their tool kits, as well as not appearing to do any actual testing, you knoe hook it up and switch on scenario, could this be that only the DAs you speak of publish YOUTUBE VIDS?? or, I suppose it's a case of the few spoiling the reputations and competences of the many, which I hope fervently is the later case.
 
Last edited:
DPG are you saying that we don’t do no kind of testing. We are not that reckless and if I wire something or do service calls I guarantee you that I know without a doubt there will be no problems. I know what I’m doing do you
[automerge]1568382086[/automerge]

I have been doing electrical work for 32 years and don’t insult my intelligence, we do have our share of dumb asses just like y’all

I'm only going on what people, including yourself, have said about testing (particularly a thread about lack of earth loop impedance testing) and also views on there being no instances of loose connections causing fires.
[automerge]1568382800[/automerge]
And of course the OP's new build wiring can't have had a thorough inspection & test.
 
I'm only going on what people, including yourself, have said about testing (particularly a thread about lack of earth loop impedance testing) and also views on there being no instances of loose connections causing fires.
[automerge]1568382800[/automerge]
And of course the OP's new build wiring can't have had a thorough inspection & test.
We ground everything and just how hard can that be. The USA is a lot more simple than the UK when it’s grounded it’s grounded and I stand by my work if you think we don’t know what we’re doing come on over and show us how
 
We ground everything and just how hard can that be. The USA is a lot more simple than the UK when it’s grounded it’s grounded and I stand by my work if you think we don’t know what we’re doing come on over and show us how

I'm not talking about whether you ground things though.
 
Megawatt, I was trying to point out that the post you took offence to was actually replying to someone else. Calm down a bit and re read the thread.
 
Yeah we certainly have our fair share Mw, although and I'm not including your good self, most of the YOUTUBE VIDS of US electricians, don't appear to have any test instruments in their tool kits, as well as not appearing to do any actual testing, you knoe hook it up and switch on scenario, could this be that only the DAs you speak of publish YOUTUBE VIDS?? or, I suppose it's a case of the few spoiling the reputations and competences of the many, which I hope fervently is the later case.
Pete I can’t speak for you tube people or any body else but I have a fluke meter, 2 meggers, rotation meter, and an AMP probe plus 2 more meters that I just have for spares
 
Pete I can’t speak for you tube people or any body else but I have a fluke meter, 2 meggers, rotation meter, and an AMP probe plus 2 more meters that I just have for spares
Ma I'm not questioning you. it was/is more a general observation from limited resources regarding US Electricians, certainly not saying that testing is better or worse than what occurs in the UK, not taking sides either.
 
We ground everything and just how hard can that be. The USA is a lot more simple than the UK when it’s grounded it’s grounded and I stand by my work if you think we don’t know what we’re doing come on over and show us how

But when it is grounded how do you prove that it is grounded with a low enough resistance?
How do you know that there is no damage to cables which are hidden?
 
But when it is grounded how do you prove that it is grounded with a low enough resistance?
How do you know that there is no damage to cables which are hidden?
I take my meter and measure the incoming neutral wire and rods in the ohms setting and usually it’s less than 1 ohm
[automerge]1568466978[/automerge]
I take my meter and measure the incoming neutral wire and rods in the ohms setting and usually it’s less than 1 ohm
We are talking about really no resistance at all
 
I take my meter and measure the incoming neutral wire and rods in the ohms setting and usually it’s less than 1 ohm
[automerge]1568466978[/automerge]

We are talking about really no resistance at all

How do you measure the rods? Presumably the direct measurement method using another substantial piece of buried metal?

What is the limit of resistance permitted for your grounds in an installation?

For a circuit breaker or fuse to work properly on a fault then the ground must be of low enough resistance.
The higher the resistance of the ground the slower the circuit breaker will react to the fault.
We have rules on how fast we need a circuit breaker to operate, in the UK this is 0.4seconds for final circuits and 5seconds for distribution circuits (there's more to it than this but I'm keeping it simple here)
So we can calculate the maximum ground resistance permitted to achieve the required disconnection time.

From this we can calculate the size of ground needed and also test it after installation to ensure compliance.

You say we are talking about no resistance at all, but that's not true, every conductor has resistance. The resistances are very small, but so are the limits for correct operation of a circuit breaker.
The limits can be well below 1 ohm and so accurate calibrated testers are needed
 
How do you measure the rods? Presumably the direct measurement method using another substantial piece of buried metal?

What is the limit of resistance permitted for your grounds in an installation?

For a circuit breaker or fuse to work properly on a fault then the ground must be of low enough resistance.
The higher the resistance of the ground the slower the circuit breaker will react to the fault.
We have rules on how fast we need a circuit breaker to operate, in the UK this is 0.4seconds for final circuits and 5seconds for distribution circuits (there's more to it than this but I'm keeping it simple here)
So we can calculate the maximum ground resistance permitted to achieve the required disconnection time.

From this we can calculate the size of ground needed and also test it after installation to ensure compliance.

You say we are talking about no resistance at all, but that's not true, every conductor has resistance. The resistances are very small, but so are the limits for correct operation of a circuit breaker.
The limits can be well below 1 ohm and so accurate calibrated testers are needed
Dave it is not letting me post my reply but table 250.102(c)(1) is how we size our grounded conductor we don’t have to run all the test that y’all do. Our house breakers are 10 RMS and they trip less than 1 second. The NEC has done all the calculations that you are talking about. We have to go by the book. Maybe this will post
 
Dave it is not letting me post my reply but table 250.102(c)(1) is how we size our grounded conductor we don’t have to run all the test that y’all do. Our house breakers are 10 RMS and they trip less than 1 second. The NEC has done all the calculations that you are talking about. We have to go by the book. Maybe this will post

What do you mean by 10RMS?

Surely you are taught the theory and science behind the tables in the book? We also have tables for selecting the size of an earth but we also can calculate it instead. The tables often end up with an earth way bigger than it needs to be.
 
Dave it is not letting me post my reply but table 250.102(c)(1) is how we size our grounded conductor we don’t have to run all the test that y’all do. Our house breakers are 10 RMS and they trip less than 1 second. The NEC has done all the calculations that you are talking about. We have to go by the book. Maybe this will post
Dave the US and the UK have different rules and as much as I have read about the way y’all have to do things I’m great full to be in the USA. We have to follow the rules set by the NEC
What do you mean by 10RMS?

Surely you are taught the theory and science behind the tables in the book? We also have tables for selecting the size of an earth but we also can calculate it instead. The tables often end up with an earth way bigger than it needs to be.
RMS is the interruption rating of the breaker
[automerge]1568472930[/automerge]
Dave the US and the UK have different rules and as much as I have read about the way y’all have to do things I’m great full to be in the USA. We have to follow the rules set by the NEC

RMS is the interruption rating of the breaker
You stated that your tables give you a size that in your mind is bigger than you need. I believe that when it comes to grounded conductor I think that it should be the same size as the ungrounded conductors
[automerge]1568473100[/automerge]
Dave the US and the UK have different rules and as much as I have read about the way y’all have to do things I’m great full to be in the USA. We have to follow the rules set by the NEC

RMS is the interruption rating of the breaker
[automerge]1568472930[/automerge]

You stated that your tables give you a size that in your mind is bigger than you need. I believe that when it comes to grounded conductor I think that it should be the same size as the ungrounded conductors
Dave I give up I know you are smarter than me when it comes to the theory of electrical
 
Last edited:

Reply to HELLO in the USA Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
486
Hello everyone. I am looking at gaining electrical qualifications in order to do installations and self certify ect. My background is...
Replies
3
Views
680
Hi everyone. I'm the landlady of Railway Inn in Winchester, a grassroots music venue. I requested to join to increase my understanding of what...
Replies
18
Views
712
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
696

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician State Laws for Electrics and Electricals may differ on a state-by-state basis. American questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock