134.2.1 of the good book tells you what you must achieve when adding too or altering an installation,it tells you how it can be achieved by test and inspection
The insulation resistance test is part of a series of tests that will verify if the standard has been complied with when adding or altering an installation
If you were to fit a consumer unit with an RCD (made an alteration to an existing installation)then the recomendations for the integrity of the insulation resistance of that installation (by comparing values with what is written in the good book )they can be verified as complying with the standard and the values that are suggested
You could even have earth leakage sufficient enough on an installation, that could trip an Rcd whether the insulation resistance was good bad or terrible
The test you are questioning is only one way of giving indication if there is system fault that would likely cause the Rcd to trip if it was fitted
The values that people have been referring too, are relevant when adding or altering an installation and initial verification,they are relevant for all work that you carry out
Thanks for your answer.
I think i now see what you and others are saying in that if you test after when you finish a job and the installation you just worked on is ****e and rigged with faults ect then they become your problem. Instead of just testing before hand so you know what your getting involved with?
What other ways could you test before fitting an rcd then?