An electrician had to install a new electrical supply to air conditioning condensors
and internal cassette
2 no 30 A supplies
1 no 10 A supply to internal unit

Instead of running these from the incoming mains board they did the following

They installed a new consumer unit along side an existing consumer unit
This ex consumer unit was some 15 m away from incoming mains and supplied by a 6 mm twin and earth cable
The new consumer unit was connected into ex consumer unit with 16 mm tails

The installation operated ok until recently

The neutral tail became loose and started arcing

I believe the 16 mm tails were connected to the same terminal as the 6 mm twin and earth

Was this installation within the regulations
Would this installation be considered "good practice"
The original works were carried out in 2006
 
The ex consumer unit was feeding a 7litre water heater and a double socket and three fluorescent lights

The cable to the condensor units was 16 mm

The 32 A fuse had never tripped over the four year period
 
An electrician had to install a new electrical supply to air conditioning condensors
and internal cassette
2 no 30 A supplies
1 no 10 A supply to internal unit

Instead of running these from the incoming mains board they did the following

They installed a new consumer unit along side an existing consumer unit
This ex consumer unit was some 15 m away from incoming mains and supplied by a 6 mm twin and earth cableIn that case the max load on this CU would be around 30-40 a
The new consumer unit was connected into ex consumer unit with 16 mm tails

The installation operated ok until recently

The neutral tail became loose and started arcing

I believe the 16 mm tails were connected to the same terminal as the 6 mm twin and earth

Was this installation within the regulations
Would this installation be considered "good practice"
The original works were carried out in 2006...No and no...clearly the existing arrangements would not be adequate for the additional load,this is a fundamental requirement of additions to an existing installation
.........
 
The ex consumer unit was feeding a 7litre water heater and a double socket and three fluorescent lights

The cable to the condensor units was 16 mm

The 32 A fuse had never tripped over the four year period

If the 32a protective device has not tripped over a 4 year period that would suggest that the DB was not overloaded as suggested in the OP....what is the running load on the A/C units?............
That said based on the info in the OP it still sounds like the existing CU is not up to running the additional loads.
 
Last edited by a moderator:

Similar threads

D
Replies
5
Views
4K
UK Electrical Forum
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Is this acceptable
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
ubrian,
Last reply from
ubrian,
Replies
6
Views
1,095

Advert