Discuss Is this allowed as i could not find an answer in the wiring regs. in the Industrial Electricians' Talk area at ElectriciansForums.net
4 core, 10mm SWA cable feeding a trace heating installation. The Installer has stated he wants to use 2 cores as 2 phases and 2 cores as Neutrals. This means the cable will have 2 separate circuits within. This would be acceptable if installed within conduit, but is this classed as bad practice within a cable??
I see no problem, as long as it’s marked correctly.
I wouldn’t call it bad practice either, efficient use of time and materials.
Be careful about method of isolation etc. And warning notes.
Thanks James, that was my first thought to have correct identification of 2 ccts at both ends.
[automerge]1570796155[/automerge]
Source URL: Is this allowed as i could not find an answer in the wiring regs. - https://www.electriciansforums.net/threads/is-this-allowed-as-i-could-not-find-an-answer-in-the-wiring-regs.179402/#post-1580921
Thanks Andy, good shout on the cpc. May require a separate earth if armour is not sufficient.
only for bonding purposes on a TNC-S. . it's adequate as a cpc, bear in mind that if you have 415V between conductors in the same cable, each conductor insulation rating must be > 415V.
No difference than multiple circuits in trunking or conduit
Labelling will be very important as will identification of cores
Make sure to correct the CCC as 2 circuits. Iz will probably work out lower than for one 3-phase 4-wire circuit as in that case theoretically no more than 3 out of 4 cores can be fully loaded (ignoring 3rd harmonic.)
Whilst I understand correct identification of conductors there is no requirement for any warning notices/labels.
Not even if they are powered from different supplies?
Isolate at more than one point type note on panel door?
Might not be a requirement but good practice where you think it is necessary.
Nothing wrong with it. Regulation 521.7 allows it as long as the requirements of regulation 528 are meant which is regarding to the proximity of other electrical and non electrical services . The only reason I know is because I carried out an EICR and had a cable with multiple circuits and questioned it myself.
Yes perfectly acceptable, it is quite clear in the regulations along with clear guidance on the applicable grouping factor.
[automerge]1573945317[/automerge]
If they are from different supplies then that would be a very different thing to just having two circuits from the same supply.
No there isn't any need for labels or notices, if there was then you'd have to start labelling every conduit, trunking, joint box, grid switch etc etc.
Plus if course there's the fact that labels and notices achieve nothing, people don't read them or take any notice of them if they do.
Reply to Is this allowed as i could not find an answer in the wiring regs. in the Industrial Electricians' Talk area at ElectriciansForums.net
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
