4 core, 10mm SWA cable feeding a trace heating installation. The Installer has stated he wants to use 2 cores as 2 phases and 2 cores as Neutrals. This means the cable will have 2 separate circuits within. This would be acceptable if installed within conduit, but is this classed as bad practice within a cable??
 
I see no problem, as long as it’s marked correctly.

I wouldn’t call it bad practice either, efficient use of time and materials.
Be careful about method of isolation etc. And warning notes.
 
I see no problem, as long as it’s marked correctly.

I wouldn’t call it bad practice either, efficient use of time and materials.
Be careful about method of isolation etc. And warning notes.

Thanks James, that was my first thought to have correct identification of 2 ccts at both ends.
[automerge]1570796155[/automerge]
Thanks James, that was my first thought to have correct identification of 2 ccts at both ends.
Source URL: Is this allowed as i could not find an answer in the wiring regs. - https://www.electriciansforums.net/threads/is-this-allowed-as-i-could-not-find-an-answer-in-the-wiring-regs.179402/#post-1580921
 
Thanks Andy, good shout on the cpc. May require a separate earth if armour is not sufficient.
only for bonding purposes on a TNC-S. . it's adequate as a cpc, bear in mind that if you have 415V between conductors in the same cable, each conductor insulation rating must be > 415V.
 
No difference than multiple circuits in trunking or conduit

Labelling will be very important as will identification of cores
 
Make sure to correct the CCC as 2 circuits. Iz will probably work out lower than for one 3-phase 4-wire circuit as in that case theoretically no more than 3 out of 4 cores can be fully loaded (ignoring 3rd harmonic.)
 
Whilst I understand correct identification of conductors there is no requirement for any warning notices/labels.

Not even if they are powered from different supplies?
Isolate at more than one point type note on panel door?

Might not be a requirement but good practice where you think it is necessary.
 
Nothing wrong with it. Regulation 521.7 allows it as long as the requirements of regulation 528 are meant which is regarding to the proximity of other electrical and non electrical services . The only reason I know is because I carried out an EICR and had a cable with multiple circuits and questioned it myself.
 
4 core, 10mm SWA cable feeding a trace heating installation. The Installer has stated he wants to use 2 cores as 2 phases and 2 cores as Neutrals. This means the cable will have 2 separate circuits within. This would be acceptable if installed within conduit, but is this classed as bad practice within a cable??

Yes perfectly acceptable, it is quite clear in the regulations along with clear guidance on the applicable grouping factor.
[automerge]1573945317[/automerge]
Not even if they are powered from different supplies?
Isolate at more than one point type note on panel door?

Might not be a requirement but good practice where you think it is necessary.

If they are from different supplies then that would be a very different thing to just having two circuits from the same supply.

No there isn't any need for labels or notices, if there was then you'd have to start labelling every conduit, trunking, joint box, grid switch etc etc.
Plus if course there's the fact that labels and notices achieve nothing, people don't read them or take any notice of them if they do.
 
Last edited:

Reply to Is this allowed as i could not find an answer in the wiring regs. in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock