Installing under sink water heaters. Each is on its own circuit and could be isolated for maintenance at the consumer unit. Do i still need to provide local isolation e.g a 45 amp dp switch ?
 
Last edited:
no.... unless manufactures instructions stipulate fitting one.
 
If the means of isolation is remote from the equipment under maintenance and therefore not continuously under the control of the maintenance operative, the supply must be prevented from being accidentally reactivated during the maintenance procedure BS7671:2008+A1:2011 537.3.1.2 This might be achieved if isolation device is capable of being secured in the open position with a suitable padlock or other simple locking method. Whatever the means of isolation it should NOT rely on the maintenance operative having to possess a specialist lock-out kit for MCBs or the like, as that is most unlikely.
 
In assuming you are not going to terminate the T+E into the water heater, you will be making a transition joint to heat-resistant flex,so use an isolator switch. :yes:
 
In assuming you are not going to terminate the T+E into the water heater, you will be making a transition joint to heat-resistant flex,so use an isolator switch. :yes:

Was thinking this myself...your going to have to joint the cable really as they usually require flex in...there usually on FCU's in my experience, out the front in flexible cable...
 

Reply to isolation where circuit serves one item of equipment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I had Scottish Power moving a supply this morning from one building to another so an extension could be built. I had everything ready for them...
Replies
1
Views
797
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
725
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
889
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock