Hello guys, and girls.
Here's the issue!
I am installing a new milling machine into a factory, the machine is specked at 32a 3 phase.
more info suggests its a 7kva machine with a 75a surge and 20kva.
so Ive calculated its basically a 5.6kw 10.64a running and 16kw 30a surge. thus the 32a mcb.
The confusion started when they were going to connect it to an existing 32a supply already installed but upon further investigation i found, yes it was a c32 and 32a isolator but the singles in the trunking were 4mm.
Now by my calculations over a 50m run this should never have been 4mm not in singles more like 10mm??
If i do a cable calc on swa armored it said 4mm (I'm using cable mate to do the calcs as its been a while since ive gone old school) now should i just rewire in a 4mm armored clipped direct?.
The cable size in the singles goes up due to the amount of other circuits in the trunking.
Ive always been taught to go worst case scenario, but am i charging the customer to install a cable that is not required?
Maybe its that the surge does not last long enough to worry about?!
Any help much appreciated but if i cannot get a final solution think ill go with my gut and put in the armored...
Here's the issue!
I am installing a new milling machine into a factory, the machine is specked at 32a 3 phase.
more info suggests its a 7kva machine with a 75a surge and 20kva.
so Ive calculated its basically a 5.6kw 10.64a running and 16kw 30a surge. thus the 32a mcb.
The confusion started when they were going to connect it to an existing 32a supply already installed but upon further investigation i found, yes it was a c32 and 32a isolator but the singles in the trunking were 4mm.
Now by my calculations over a 50m run this should never have been 4mm not in singles more like 10mm??
If i do a cable calc on swa armored it said 4mm (I'm using cable mate to do the calcs as its been a while since ive gone old school) now should i just rewire in a 4mm armored clipped direct?.
The cable size in the singles goes up due to the amount of other circuits in the trunking.
Ive always been taught to go worst case scenario, but am i charging the customer to install a cable that is not required?
Maybe its that the surge does not last long enough to worry about?!
Any help much appreciated but if i cannot get a final solution think ill go with my gut and put in the armored...