I have to move a Consumer unit approximately 6 mts. Had suggestion buy NAPIT technical to fit enclosure with terminal rail and terminals and then extend cables to new consumer unit. As the enclosure will not be readily available the terminal method would not be Maintenance Free. (If there was a problem in the future access to the enclosure could be achieved but would make a mess of decoration) Is there a Maintenance Free enclosure that will take multiple cables on the market? Or is it multiple J803 and the like. Anyone done something similar?



AdieB
 
You have all the Qualifications needed the Adie what are they exactly?
 
I had to extend an installation replacing a consumer unit last week. Not quite that long, but I used Wagoboxes, installed in maintenance free mode (i.e. with required de-rating and ensuring maximum aggregate current was not breached as I used one box for a couple of circuits) in an accessible location (in the ceiling void above the CU) and documented it on the EIC for the work.

And I concur with Midwest... if it's got screws in it, it should be accessible.
 
Even with Wago cage clamp connectors (there're other manufacturers), the enclosure should be accessible IMO. If this is not achievable, look at other methods as SparkyChick suggested, or partial rewire of feeds to RFC, Radials etc.

Anyhow, my soufflés are in the oven, and I'm just have 5 mins before I need to prepare my Béarnaise sauce for my Chateaubriand. We having fried Mars Bar for pud. :)
 
I have to move a Consumer unit approximately 6 mts. Had suggestion buy NAPIT technical to fit enclosure with terminal rail and terminals and then extend cables to new consumer unit. As the enclosure will not be readily available the terminal method would not be Maintenance Free. (If there was a problem in the future access to the enclosure could be achieved but would make a mess of decoration) Is there a Maintenance Free enclosure that will take multiple cables on the market? Or is it multiple J803 and the like. Anyone done something similar?



AdieB
Where do you intend to fit the extension box?
 
I have to move a Consumer unit approximately 6 mts. Had suggestion buy NAPIT technical to fit enclosure with terminal rail and terminals and then extend cables to new consumer unit. As the enclosure will not be readily available the terminal method would not be Maintenance Free. (If there was a problem in the future access to the enclosure could be achieved but would make a mess of decoration) Is there a Maintenance Free enclosure that will take multiple cables on the market? Or is it multiple J803 and the like. Anyone done something similar?



AdieB

Hum.......
 
Metal enclosure, DIN rail Wago connectors, or DIN connectors
If you absolutely have to have it non accessible due to decoration and all, I would go with Pete's idea as Wago on a DIN rail will be maintenance free and the non combustible enclosure will take care of the other regulation requirement. Just make top job of it and document it well with photo on EIC.
 
Asked my Scheme recently, their opinion on such an enclosure as to whether it would be classified as 'similar switchgear', as described in reg 421.1.201.

''This will be the decision of the designer but it would suggest based on our guidance in this situation the enclosures and connections do not fall under 'similar switchgear''.
 
Asked my Scheme recently, their opinion on such an enclosure as to whether it would be classified as 'similar switchgear', as described in reg 421.1.201.

''This will be the decision of the designer but it would suggest based on our guidance in this situation the enclosures and connections do not fall under 'similar switchgear''.
Good bit of buck passing by your Scheme there Middy
 
You have all the Qualifications needed the Adie what are they exactly?

I am of the older generation. I have A B & C and 17th Edition City and Guilds I also have the inspection and Test certificate and have been in the electrical industry since 1973 when I did my indentured apprenticeship. I am a also registered with NAPIT.
 
The meter has already been moved and new tails installed . In the meter box due to the length of the tails an 100A isolation switch has been fitted.
 
The meter has already been moved and new tails installed . In the meter box due to the length of the tails an 100A isolation switch has been fitted.

Is that a switch fuse with a 100A fuse or just an isolator rated at 100A? If the tails are over 3m it will need to be a switch fuse.
 
The other option which nobody has mentioned so far is soldered or crimped joints with a liberal application of suitably rated heat shrink sleeving. Just a thought.
 
The extension box is in place of the old consumer unit. the cables will then extend to the new consumer unit location
In that case the connections would be accessible wouldn't they? ergo no need for MF connectors.
 
Thanks guys, in the words of everyones favourite meerkat... Simples! :)

I was over thinking it when you mentioned the enclosure @Des 56

Soldered joints, whilst they are very familiar to me as a result of my experience building public facing cash handling/ticketing machines and other electronic gizmos, they are my last resort for this sort of thing. I've only had to use one thus far where some plumb had left about 1.5" of cable sticking out the wall for an outside light with no slack and that ended up enclosed by the replacement light.

When I wrote my original comment about the heatshrink I nearly edited it to state the shrink should be adhesive lined to provide some strain relief for the joint hence my question, and I committed what turns out so often to be the cardinal sin... I assumed... in this case that the cables would be in a ceiling void or chased into a wall. And on that note, would the ceiling void constitute a suitable enclosure under 526.5 Item iii, providing the the plasterboard is BS 476-4 compliant?
 
And on that note, would the ceiling void constitute a suitable enclosure under 526.5 Item iii

Not being a legal eagle,its never easy to put a definitive interpretation of the regulations that is agreed by all

With the ceiling void,my own belief is "no it is not an enclosure" in the electrical connection sense,but it is an enclosure perhaps in the fire safety world

My reason for not considering the ceiling an enclosure is that someone can access the void with no intention or expectation of it containing unprotected cables,an example being the connector blocks and tape used for fancy light fittings
With that I rest my case your honour
 
Agree. For me it's not an electrical enclosure if it doesn't look like an enclosure ( e.g. roof space) and or you can access it without a tool (e.g. plastic food container ... yep seen takeaway food box repurposed once, well it was near the kitchen to be fair :) ).
 
Not being a legal eagle,its never easy to put a definitive interpretation of the regulations that is agreed by all

That is so true.

My reason for not considering the ceiling an enclosure is that someone can access the void with no intention or expectation of it containing unprotected cables,an example being the connector blocks and tape used for fancy light fittings
With that I rest my case your honour

And there I guess is the issue in this particular example... what constitutes unprotected? I would have said, soldered joint, with adhesive lined shrink over individual cores and then an overall adhesive shrink encasing the basic insulation and inner shrink, extending by say 0.5" over the outer sheath would constitute 'protected'.

As for the terminal blocks wrapped in PVC for fancy lights... I totally agree, not enclosed. The best (or worst, depending on which way you look at it) example I've encountered was actually at home, where some plum had installed an electric shower by stripping the insulation off the cooker feed and had simply wrapped the shower cable around the cores with a liberal application of tape. I had no clue it was there and was feeling around in the floor space trying to locate the junction box, because it never crossed my mind that anyone would have been so stupid... didn't get me, but taught me a valuable lesson none the less. Always look before you feel ;)
 
That is so true.



And there I guess is the issue in this particular example... what constitutes unprotected? I would have said, soldered joint, with adhesive lined shrink over individual cores and then an overall adhesive shrink encasing the basic insulation and inner shrink, extending by say 0.5" over the outer sheath would constitute 'protected'.
;)

Yes,to me the above example would give the impression of being well insulated, :thumbsup: but here is the however

It seems that a cable that has had the insulation removed,the new insulation should provide at least the the same degree of protection as the original,can we guarantee that is so with our own efforts :)

Always look before you feel ;)
My wife tells me that
 
My 20p on heat shrink is it's a good start, but it's not same standard as the original cable so needs additional containment / protection. Just my opinion:)

Yes,to me the above example would give the impression of being well insulated, :thumbsup: but here is the however

It seems that a cable that has had the insulation removed,the new insulation should provide at least the the same degree of protection as the original,can we guarantee that is so with our own efforts :)

Nicely explained guys and thanks for entertaining my questioning :) Much appreciated.
 

Reply to Moving Consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
6K
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock