My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated. Research says I need an IP44. The lamp is about 2.45m above the floor and about 30cms outside the side of the bath. Has he made a mistake or have I?
 
This is really up to the inspector to decide.

Although technically outside any of the zones, being above 2.25m from the floor, (and therefore not required to comply with zoning regulations) the light still has to be suitable for the environment it is installed in.

If the light was in zone 2, then the MINIMUM applicable IP rating would be IPX4. If it was possibly subject to splashing of water from a shower head, then the minimum would be IPX5.
 
This is really up to the inspector to decide.

Although technically outside any of the zones, being above 2.25m from the floor, (and therefore not required to comply with zoning regulations) the light still has to be suitable for the environment it is installed in.

If the light was in zone 2, then the MINIMUM applicable IP rating would be IPX4. If it was possibly subject to splashing of water from a shower head, then the minimum would be IPX5.
The light is nowhere near any source of water. My confusion is why he said the fitting must be IP65, not IP44 (or IPX4) as in the regs. I'll try to post a photo.
 
Had a similar scenario and our NIC inspectors argument was that it was reachable from the bath and an enclosed fitting would be an improvement so RCD protection aside C3
 
Here is a photo of my bathroom light fitting.
20221024_145949.jpg
 
Last edited by a moderator:
So if the standard light fitting is probably only IP 20 and above 2.25M of Zone 2, then how would you code it, & maybe it is RCD protected as well?
I sometimes come across metallic fittings that are not in any zone but are corroded. In this case I might C3 them, as they are clearly unsuitable for their environment.

In some cases I might choose not to allocate a code, but add a comment in the report that, in my expert opinion, the light is not suitable and should really be changed.
 
That may well be a suitable fitting, is there a seal between glass and base?

Biggest problem with this type of enclosed fitting is unprotected/wrong cable, ie overheating becoming brittle. 100w lamp fitted when max should be 60w!
 

Reply to My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have 16 ceiling spots to be replaced in a room being repurposed as a bathroom. Some will be over a shower, basin and bath hence need to be IP65...
Replies
19
Views
981
Hi all, I'm refitting my bathroom in my first floor flat (top floor) built around 1989. It has 2 CUs, one for night storage and one for 24h...
Replies
39
Views
4K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
673
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
D
I've booked in an electrician to run an EICR, I have an old unit here, whilst searching for quotes one guy said it looks ok and may not need...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock