Hello,
I have a brand new Indesit standalone ceramic hob oven installed with own mcb and new wiring (surface trunking) and cooker switch and socket both neons. The ccu is part rcd protected. The mcb is not on the rcd side. When power is applied to the cooker, the time flashes 0.00 and then I set the time. When any of the hobs are switched on, the rcd trips. Switching off the hob, the time is reset to 0.00. Tried resetting the time 2-3 times but when any of hobs switched on, rcd trips again.
Checked the voltage to the cooker switch =240v. With the cooker disconnected, v=240 on the load side (cable unplugged) indicating the neon is also not causing problem. With the cooker plugged in, the load side shows the voltage has dropped to half.
Called indesit and they sent an engineer (who said his son was part P, can't remember whether he was part p or not or even qualified electrical). He immediately blamed my wiring as a short circuit. I mentioned that if there was a short, the mcb will not come on even without the appliance connected, as it was possible to switch on the mcb. He did the testing on this meter, when circuit not on and insulation resistance was 999, When the appliance is connected its less than 1. On his notes he mentioned it was meant to be more than 3 minimum. (the minimum is 1M, but I didn't tell him). He then blamed mcd and cooker switch (both changed and it still the same problem. He also said the appliance will work off a 13A plug (the manual recommends a minimum of 32A). :cuss:I think Indesit needs to vet and train their engineers!!!!! and tell them to read the manual before attempting to service their appliances.
Its a hager board with neutral bar coming out of the rcd for all circuits, rcd and non rcd. Can this be the problem? Rcd will only trips if there was earth leak, True?
Any help appreciated?
mcb is overload not shortcircuit device, get a proper electrician in . the cooker with a correct mcb hould be on the correct rcd, the one you have may be faulty
Should the cooker be on the rcd side? The wiring is surface mounted. Just a thought. Daz
He did IR with the hob connected?! Unless he interlinked the line and neutral of course he's going to get odd results, and if he DID link out he was never going to find a line to neutral fault anyway...
Hello,
So is the hob going to be replaced under the warranty??
The 3 Meg he was talking about, is probably that stated by the manufacturer for this hob appliance. The 1 meg your talking about is for building wiring....
Neutral in wrong bar in CU. 99%.
or incorrectly set up CU. you can't have the N coming out of the rCD and the L not.
'jeffelectric 'mcb is overload not shortcircuit device, get a proper electrician in . the cooker with a correct mcb hould be on the correct rcd, the one you have may be faulty'
Read the post correctly. I did mention both the mcb and the cooker switch were changed. They might also be faulty. very unlikely.
What do you mean 'the cooker with a correct mcb hould be on the correct rcd'? Its got its own mcb. rcd is shared across with other circuits or did you expect rcd for individual circuits. Its not rcbo. I hope you know the difference???
You go straight for mcb not an overload device hoping no one might notice and not reply back, then you change your story once you have been noticed, blaming on fast typing. think you need to leave electrics well alone if you do not understand the principles. And don't bother giving advice either!!!! Unlike you I knew what I am doing and typing.
'telectrix 'or incorrectly set up CU. you can't have the N coming out of the rCD and the L not.' They are both coming out of the rcd 2 ingoing 2 outgoing. Its split board. some rcd protected and some not protected But there in only neutral bar which is serves all circuits whether rcd or not.
'Engineer54' So is the hob going to be replaced under the warranty??
The 3 Meg he was talking about, is probably that stated by the manufacturer for this hob appliance. The 1 meg your talking about is for building wiring....'
No mention of returning it or changing it. As mentioned in the post he blames wiring, then the mcb or the switch.
There is no mention in the manual about the 3 meg but he did not mention this either.
It can be changed to rcd side. But I need to sort out this first. I do not want rcd tripping when connected to the rcd circuits.
What a rude reply. If you know what you are doing then good luck to you, as you obviously don't need any more help. Daz.
If the MCB supplying the hob is not on the RCD side of the board then the RCD should not trip in any event of a fault with the hob or hob wiring. As telectrix says, there can only be something wrong with the consumer unit arrangement. You will need to have it checked by a pro.
From what I read, this is your answer.
you say your MCB is NOT on the Rcd, but your neutral is. So you will be causing an imbalance across the Rcd, put the mcb onto the Rcd protected side of the CU, that should sort things as both neutral and live will be from the RCD protected side of the board.
may be with your next reply you could include a picture of your board with the cover off
you can't have RCD protected circuits and non -RCD protected circuits using the same neutral bar. end of. is this clear enough?
Hi,
As Telectrix says, Neutral problem. On the Hager Board there are three 'bars' at the top, maybe all the Neutrals have been put in the centre earth 'bar'; and the earths into the two neutral 'bars'?
Regards.
just occured to me. some boards come with 2 N bars linked together. is this the case and that the link needs removing?
a photo of the CU ( cover off ) would show.
Not really, any chance of typing it in bigger font :)
Surely if all circuit neutrals are sharing the same bar in the CU, including the ones supposedly protected by the RCD, wouldn't he have had nuisance tripping before now?
Reply to New standalone ceramic hob oven keeps tripping rcd in the UK Electrical Forum area at ElectriciansForums.net
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...