R

Richard3009

A property has 10 radial circuits supplied off an old Economy 7 off peak board that used to feed storage heaters, they are now converted to 10 individualy fused radial 13A socket outlets. The owner wants you to replace both of his consumer units, where you going with this. Circuit id and isolation could be a future risk, take out radials or re_instate.
 
A property has 10 radial circuits supplied off an old Economy 7 off peak board that used to feed storage heaters, they are now converted to 10 individualy fused radial 13A socket outlets. The owner wants you to replace both of his consumer units, where you going with this. Circuit id and isolation could be a future risk, take out radials or re_instate.
I dont understand this bit?
 
A circuit can comprise of 1 or more cables at a MCB so I'd see if they could be "grouped" and put them on 20A MCB's - if not you are going to need a very big CU
 
My biggest concern would be a future person could isolate the downstairs ring main and think every socket to be dead, I know test for dead and all that, but this one could bite somebody
 
My biggest concern would be a future person could isolate the downstairs ring main and think every socket to be dead, I know test for dead and all that, but this one could bite somebody

I don't think that this is an issue, especially if there's some indication on the circuit labelling that the main socket circuit doesn't include some of these ex-storage heater sockets.
 
Could you not print something or use a label machine and place near consumer unit explaining about lots of radials so isolate all socket circuits or something similar
 
  • Like
Reactions: 1 person
good point, from what I can see there is nothing in the regs to stop you stuffing many radials into one mcb, although not good practice.
 
multiple circuits into one MCB hmmmmmmm

Not multiple circuits; one radial circuit with multiple branches. Nothing wrong with that.

Edit: providing that the terminals can take the cables and still make an acceptable connection.
 
Is this a wind up?

Radial circuits feeding sockets are perfectly normal and as long as they meet the requirements of the regulations then leave them as they are.

The circuit list you fix at or near the consumer unit will make it perfectly clear to anyone working on the installation won't it?
 
  • Like
Reactions: 1 person
You really are making a mountain out of a mole hill.

One net circuit is one MCB in this instance, regardless of how many branches there are at the MCB.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Old storage heater radials.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
Richard3009,
Last reply from
HandySparks,
Replies
33
Views
3,881

Advert