I have to run a 70mm SWA sub circuit over a distance of 70metres in a 4in duct under ground. The cable will run from the main incoming electricity boards supply (busbar after meter). I know I will need an isolator at the front but do I need an RCD also, like a 100mA time delay???
Current being drawn will be around 120A max. The install is on a farm and the supply is a 200A CT monitored single phase TNS supply.
If anyone can point me in the right direction regarding the correct chapter in the regs it would help, if its the case I need the RCD!!
 
Special Locations: Agricultural and Horticultural Locations.
 
I believe the requirements for RCD protection in Agricultural/Horticultural premises are:
30mA for circuits supplying socket-outlets (32A and below), 100mA for circuits supplying socket-outlets above 32A and 300mA for all other circuits.
Obviously this is dependant upon Zs being low enough for the RCDs to operate.
 
The SWA cable buried in ducts at the correct depth as laid out in the regs would not need RCD protection , how ever circuits from the consumer unit it supplies will depending on the installation methods and useage check out section 705 page 216 of the regs , you will need a switch fuse however to protect the cable so as not rely on the supply fuses
 
Last edited by a moderator:
  • Like
Reactions: 1 person
705.411.1 In cicuits, whatever the type of earthing system, the following disconnection devices shall be provided:
(i) In final circuits supplying socket-outlets with rated current not exceeding 32A, an RCD having the characteristics specified in Regulation 415.1.1
(ii) In final circuits supplying socket-outlets with a rated current more than 32A, an RCD with a rated residual operating current not exceeding 100mA
(iii) In all other circuits, RCDs with a rated residual operating current not exceeding 300mA.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD or NOT???
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Reg Man,
Last reply from
Guest123,
Replies
5
Views
1,736

Advert