Hi all,
At my place of work there is a newly built primary school. I carry out the maintenance on his building and at the beginning of the year the heating was shut down to the building to allow work to be carried out and also this shutdown is normally done during summer months. However, we had a spell of cold weather and this meant the corridors and places where the year 1 kids sit was too cold. (about 10C)
The contracts managers wouldn't allow us to install additional fused spurs for heaters (still within warranty) so the only option to get a temporary form of heating was to install some Dimplex FX20V 2Kw downflow heaters. These were wired in 1.5mm 3 core flex, about 2m down wall in mini trunking onto a 13amp plug and plugged in to the socket outlet.
The issue now is another manager from the main school has said "this is against NIC primary school regulations. They should be hard wired in via fused spurs." Correct me if I'm wrong but I've never seen NIC Primary school regulations.
The only regulations I can find (I only have the red book at home) are:
521.9.3 - A flexible cable or flexible cord shall be used for fixed wiring only where the relevant provisions of the regulations are met.
530.4.1 - Except where specifically designed for direct connection to flexible wiring, equipment shall be fixed according to manufacturers instructions in such a way that connections between wiring and equipment shall not be subject to undue stress or strain resulting from the normal use of the equipment.
Now the heaters are not classed as fixed wiring by being on a plug and were PAT tested prior to using them.
Does any one know if these heaters are against regulations wired in this way? Or if there any regulations that will be against this setup?
I am aware its not ideal but were installed as a temporary use thing, but then again this is no excuse to not follow regulations.
Thanks for the help in advance
At my place of work there is a newly built primary school. I carry out the maintenance on his building and at the beginning of the year the heating was shut down to the building to allow work to be carried out and also this shutdown is normally done during summer months. However, we had a spell of cold weather and this meant the corridors and places where the year 1 kids sit was too cold. (about 10C)
The contracts managers wouldn't allow us to install additional fused spurs for heaters (still within warranty) so the only option to get a temporary form of heating was to install some Dimplex FX20V 2Kw downflow heaters. These were wired in 1.5mm 3 core flex, about 2m down wall in mini trunking onto a 13amp plug and plugged in to the socket outlet.
The issue now is another manager from the main school has said "this is against NIC primary school regulations. They should be hard wired in via fused spurs." Correct me if I'm wrong but I've never seen NIC Primary school regulations.
The only regulations I can find (I only have the red book at home) are:
521.9.3 - A flexible cable or flexible cord shall be used for fixed wiring only where the relevant provisions of the regulations are met.
530.4.1 - Except where specifically designed for direct connection to flexible wiring, equipment shall be fixed according to manufacturers instructions in such a way that connections between wiring and equipment shall not be subject to undue stress or strain resulting from the normal use of the equipment.
Now the heaters are not classed as fixed wiring by being on a plug and were PAT tested prior to using them.
Does any one know if these heaters are against regulations wired in this way? Or if there any regulations that will be against this setup?
I am aware its not ideal but were installed as a temporary use thing, but then again this is no excuse to not follow regulations.
Thanks for the help in advance