albi

-
Reaction score
7
After a pir has been done and you carry out the repairs detail on the schedule do you then issue another pir as no new circuits have been installed only extra bonding to bring the Zs reading down and fitting banjos to swa cables and replace 2 mem switch fused isolators due to broken covers
 
You may have answered your own thread with the bonding. Was it just fitting new 10MM^ bonds or was it just replacing old with 10MM^

I would leave the PIR as is, as that was what the installation was when you did it. For the bonding fill out a minors work certificate which will be put with the PIR paperwork and at the next PIR date whoever is doing it will see that the MWC is after the PIR and work accordlingly.

Also if it's domestic you don't have to certify maintenance or bonding as Part P
 
no main bonding still in place and its in a warehouse from the 1970 they have used the armouring on the sub main cable as the earth so we fitted a 95mm to the board to the steel work as its a good run back to the mains (95mm was left over from another job so used it)
 
depending on what work is done a minor works if its replacing "like for like" if you are changing caracteristics then an EIC for that circuirt The bonding probably a M/W and as Malcom says Put copy of PIR and M/Ws together if its commercial all certs should be kept together anyways
 
I'm assuming then that your PIR prooved the SWA armour was ok, as it was a sub main cable you took the R1 + R2 or the Zdb to prove your Zs readings and did your Zs reading fail as you mentioned to bring them down?

If the Zs failed on the PIR then that should have been coded as a 1 and the PIR should not have been completed until this was rectified.

If your saying that at the PIR the Zs was ok and proved disconnection but now your wondering if the Zs will have changed due to Parallel paths. If so then as I said leave the PIR as is, but on a MWC note that you have altered the bonding.

Lastly you said that you have now bonded the steel work with that 95mm^ did you take it back to the MET at origin. All bonding must go back to the main MET unless it is supplementary bonding as in bathrooms. You may have to consider running that back to the MET as I think steelwork is classed as main bonding.
 
I believe it should be coded of as a 2 as there is no immediate danger of any one getting a belt. The main bonds are in place and all I have done is made a parallel path using the steel work. the sub board past the it was the circuts in the board that faild. mainly 3 phase type c mcb's to moters every thing ealse was fine. now i have this earth in place the readings on the circuits now are withing range.
 
Last edited:

Reply to repairs after pir in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
467
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Can you be taken to court for an EICR by a house purchaser 13 months after EICR was issued, house purchaser has had there own report done 13...
Replies
21
Views
4K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock