Hi
There seems to be some confusion at work about ring circuit continuity on an EICR. I was under the understanding that you took r1 & r2 added together and divided by 4, then during the live testing a Max Zs was measured using meter. The method two or 'figure of eight' is used only on Initial Verification or where there is no supply present.
This appears to be reinforced in both the old periodic and the new EICR dvd's created by the NICEIC where Tony Cable and his sidekick confirm that the figure of eight method is not requires on an EICR.
Why then do supervisors and inspectors insist on this method being used ?
Anyone able to enlighten me.
It appears to be the age old politically correct method v the financially viable method again !
Regards
Guffer
Sorry mate, somehow I missed that post
Thanks for the replies but we seem to be missing the point, its not do we do a figure of 8 as good practice, its do we HAVE to do one on an EICR ?
If we do, why do both NICEIC dvd's make a great point of telling us we dont.
Thats what i cant understand ?
Which DvD is it that says this mate? I've not seen any of them and if I can catch a copy of it on youtube I'm going to email them to ask why they think a fundamental test is not necessary. I'll need to have the facts at hand before I open my trap though.
The NICEIC have released two DVD's for periodics, the older of the two is called 'Domestic Periodic Inspection Testing and Reporting' look round about the 40 minute mark and the more recent is called EICR 2011 with the juicy bit 59 minutes in.
There's no question of misinterpretation either, both scenes clearly state figure of 8 not required ?
Not much has changed with periodics then, still a lot of misunderstandings.
GN3 is well worth a read, but even this won't clear things up any better. The main reason for carrying out periodics, is to ensure that the disconnection times can be met.
What you test and how you test it is left to your discretion depending on your initial findings, and chosen sample for what you see, and what if any records are available.
So even though we all have our own ideas and opinions, no one is really right or wrong, but i will go with testing the sampled circuits properly and fully for reasons that have been mentioned in earlier posts.
Cheers………….Howard
I seem to remember a suggestion that ring circuit continuity does not have to be tested where there has been no alterations or additions to that circuit since a previous test and an installation certificate or EICR is available with the results
Here's a thought Why dismantle a circuit to verify what is already known
Des you are bang on, and it also says that careful consideration should be given before dismantling or removing accessories as you could make a bad situation a lot worse. Some things are better left alone.
Cheers………..Howard
the only reason i can think of is possible alterations that may not be visible
(ive seen this on a home inspection where a furnace transformer was hidden behind a plaster board wall)
Fair comment Gnuuser
Question to you, I thought ring finals were not used in that grand country of yours
I think my statement could be used in commercial or industrial situations where procedures are monitored
However,for a domestic customer or other less strict ind/com I would not heed my own suggestion
true almost all our systems are radials but on occasion i find some old houses wired with ring circuits (not very often though)
haha at first time i found one in an old house(way back when i was an apprentice) i had a hell of a time figuring out why it had power on both ends of the hot core when they were unhooked
the master was laughing his butt off
he knew what it was as soon as he saw the readings on the meter
we used to test the cores for the live one and label it for supply
Reply to Ring Circuit Continuity on EICR (Figure of 8 ?) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Hi All, Many of you have been assisting me with a different EICR issue. Your contribution has been invaluable. This post is not related to that...
5K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Hi, With Referance to the current Initial verification and periodic practical exam. Continuity of protective conductors, including main and...