Hi,
With Referance to the current Initial verification and periodic practical exam.

Continuity of protective conductors, including main and supplementary bonding.

I understand using method one with circuit c.p.c, Connect line/c.p.c in connector blocks. Results provide, continuity, R1=R2 and polarity.

I understand method two for Main bonding. Remove cable from DB’s earthbar, test between cable and earth clamp at Extraneous conductive part.

However, on 3-phase DB,(periodic test)
3 phase Armoured circuit to 63 amp socket, for motor, via DOL. The Armoured’s sheath is conductor.
Also, MI cable to FCU for water heater. The Mi’s metal sheath is a conductor.

I can do Method one for the 3 core and MI circuits.
Should I also do method two between DB’s earth bar and Armoured gland. Same for MI circuit. What are the expected results and where to record on Forms/Schedules of test results?

In addition, Supplementary bonding connected between extraneous conductive water pipe and water heater spur mentioned above? Test between earthclamp and spur faceplate…Expected result is 0.05 Ohms? Where is this recorded?

Further,
the single phase cu, sub-main, (initial verification). It’s circuits are house in Metal trunking/pipe/metal clad switches and socket.
Therefore? Method two between cu’s Earth bar and various locations for said metal equipment?
Again what are the expected results and where to record?

Thank you.
 
Which ever method you decide to use to measure and record continuity, null out first, there is a lot going on behind the board you see. When I did 2391-52 two of my readings were massive due to resistors suitably placed.
 
Hi,
With Referance to the current Initial verification and periodic practical exam.

Continuity of protective conductors, including main and supplementary bonding.

I understand using method one with circuit c.p.c, Connect line/c.p.c in connector blocks. Results provide, continuity, R1=R2 and polarity.

I understand method two for Main bonding. Remove cable from DB’s earthbar, test between cable and earth clamp at Extraneous conductive part.

However, on 3-phase DB,(periodic test)
3 phase Armoured circuit to 63 amp socket, for motor, via DOL. The Armoured’s sheath is conductor.
Also, MI cable to FCU for water heater. The Mi’s metal sheath is a conductor.

I can do Method one for the 3 core and MI circuits.
Should I also do method two between DB’s earth bar and Armoured gland. Same for MI circuit. What are the expected results and where to record on Forms/Schedules of test results?

In addition, Supplementary bonding connected between extraneous conductive water pipe and water heater spur mentioned above? Test between earthclamp and spur faceplate…Expected result is 0.05 Ohms? Where is this recorded?

Further,
the single phase cu, sub-main, (initial verification). It’s circuits are house in Metal trunking/pipe/metal clad switches and socket.
Therefore? Method two between cu’s Earth bar and various locations for said metal equipment?
Again what are the expected results and where to record?

Thank you.
might want to look at this vid
 

Reply to Continuity of protective conductors...Initial/Periodic exam. in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hope i find someone who can help me with this one. I have this question on an exam: A continuity test on a protective bonding conductor gives a...
Replies
7
Views
5K
I sat the 2391-52 Initial Verification & Periodic Inspection and Testing online Exam last week and failed by 1 mark. I got 100% in 2393-10 and 90%...
Replies
1
Views
4K
Hi guys, QUESTION: Do you test the suppliers earth conductor for continuity??? The guidance note 3 2.6.5 refers to regulation 643.2.11 which...
Replies
2
Views
2K
This may seem like a stupid question but when testing for continuity using the long lead method I know you test the water and gas bonds etc but do...
Replies
5
Views
2K
Afternoon all, How do i solve these two questions, Feel like am missing something simple. doing my head in lol. I need to learn the calculation...
Replies
24
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock