stevie h

Doing a rewire at the mo , its my 1st one under the new regs , going to use a 17th edition double split RCD board , are the mains smokes ok to go on one side of the board ? or do they need to go on there own RCBO

Cheers

Ste
 
i'm a bit confussed, can a smoke detector be protected by an rcd on the smoke detector's own circuit. if the smoke detector has its own battery backup, can it be still be protected by rcd. Part P does state it should be on its own circuit, but should it be RCD protected. I'm thinking if if was and the RCD tripped and the battery was dead, then that smoke alarm would not work.
 
smokes only require RCD if the cable/s are buried <50mm deep without earthed mechanical protection.
 
I understand the Logic in this, But irrespective of where the Smoke detector circuit is placed it still has to have a means of isolation of its own..So surely the circuit could be turned off anyway???

Not so. This 'advice' is in AD-B, where the wording is 'should' not 'must'. Anyway you could still take the smokes supply back to the MCB and label the leg - not easy for the average owner to 'turn off' but still complies with AD-B advice
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Smoke detectors + 17th edition
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
23
Unsolved
--

Advert

Thread statistics

Created
stevie h,
Last reply from
Spudnik,
Replies
23
Views
9,304

Advert