why would a load need to be midway in a ring to avoid overloading??that's the point of a ring, that every point is the same in regards to any load upon it.I find that worrying that someone would think otherwise

You seem to be missing something quite significant, not to mention basic about RFC's and that is this:

The relative currents in each leg of the ring supplying the socket in question (where ever it may be on the ring) are split in inverse proportion to the relative resistances of said legs. In other words, apart from the exact middle of the ring, where the legs are of equal length, current will not flow equally down each leg, but will be relative to the resistance of that leg. i.e longer leg, more resistance, less current.

Simply put, you are incorrect, and Spin is correct.
 
Have you EVER given a useful piece of advice to anyone? or do you get your jollies by trying to appear superior to everyone else? do us all a favour and get a life. I've been an electrician most my life and know what a ring should be wired in. I was simply wondering about any options in regards to the flex.noone has yet proved that it's against the regs but I know it'll have to go

While I am in no way the most learned or intelligent electrician on this forum (in fact there are many here who I consider far more knowledgeable than myself), I like to think that I have helped a few people with their issues and problems. We all need help occasionally, but when a so-called qualified electrician comes on here asking what to do with a 1mm kitchen socket circuit, and then asks what size MCB might make it all ok, are you really so surprised at some of the responses?
I would suggest that you re-read your original post from the perspective of someone who doesn't know you at all, and you might see why we are all so concerned on here.
As to your suggestion of me "getting a life".... I think that I have a very good one thank you. :)
 
There are four options:
1) Rip out and replace.
2) De-rate the CPD.
3) Disconnect and leave alone.
4) Leave as is and do nothing.
You've already stated that ripping out and replacing is not an option.
It's been pointed out to you what the maximum rating of CPD should be if you de-rated, but you appear to be having trouble understanding the reasons.
That leaves you with disconnection or leaving as is.

Just to set your mind at rest, as has already been pointed out by others, there is nothing in the Regulations prohibiting the use of flex for fixed wiring.
The only reason (from the information you have provided) that the situation doesn't comply is that the CPD is rated too high for the conductors used.


And on that clear & concise bombshell, it's time to end.

Thank you so much for reading, good night.:driving:


***Thread Closed***
 
New posts

Reply to sockets wired in 1.0mm 3 core flex in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Was wondering if you could help please. I'm looking to fit a BG IP66 external socket mainly for occasional jet wash/vacuum usage and...
Replies
9
Views
1K
I have a spare 2.5mm 3 core flex cable. Can I use it for an outdoor light? It will be connected a junction box that's already supplying...
Replies
2
Views
911
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock