How's this for a means of earthing this steel conduit is acting as a tt arrangement, although brilliant ze readings, 6.41 ohms 34a. What do you all think to this.
 
Are you sure that's conduit?
 
The suppliers cables are installed within this containment, it's definitely not lead sheath
 
Looks like 1" conduit to me, not sure about the tt bit, does the conduit go underground? If so it'll no doubt be corroded as it's b/e, not a good idea at all!
How have you conducted your tests?
 
Just been thinking about this. At my Grandfathers farmhouse the electricity boards supply did enter the building as VIR’s in conduit. That was from the OH supply at the end of the building. It ran along the front of the house.

Not bad remembering that, I was seven when he died.
 
  • Like
Reactions: 1 person
Yes the conduit goes into the ground, no way will I get a better Ze reading with a earth rod, just wondered if any1 else has come across this
 
Looks like 1" conduit to me, not sure about the tt bit, does the conduit go underground? If so it'll no doubt be corroded as it's b/e, not a good idea at all!
How have you conducted your tests?

Disconnected main earth and carried out EFLI test on high current
 
Yes the conduit goes into the ground, no way will I get a better Ze reading with a earth rod, just wondered if any1 else has come across this
your misses will know the answer


deeper lol
 
Disconnected main earth and carried out EFLI test on high current

Disconnect bond on that copper pipe and see what you get. lol Bet it won't be so good.
 
I stand by my last post no way is that conduit, just look at the tee off
 
Looks like 1" lug grip conduit to me, held to the wall with crampets. Can't see if the tee is an inspection type - it seems to have the outline of a cover. The stub above the tee seems to have a rubber female bush where cables used to exit.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Steel conduit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
Buzz-light-bulb,
Last reply from
Lucien Nunes,
Replies
21
Views
3,603

Advert