Bengaz

-
Reaction score
0
Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth electrode to each unit. Did anyone know that? The NICEIC tech help didnt today...

Even though NPG supply a MET cant be used.

A break in the neutral supplying any unit and the current would flow through the frame and back to the transformer via the PME link in an adjacent unit. You may never know there was an external fault.
 

Attachments

  • WhatsApp Image 2024-02-27 at 19.25.05_c8b37768.jpg
    238.6 KB · Views: 19
Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth electrode to each unit. Did anyone know that?

Yes, this is standard practice with all DNO's, I think may even be derived from ESQCR or something like that.


The NICEIC tech help didnt today..

Say no more.

.A break in the neutral supplying any unit and the current would flow through the frame and back to the transformer via the PME link in an adjacent unit. You may never know there was an external fault.

It's worse than that, the normal neutral currents of each installation will be diverted via the steel structure of the building via the bonding and back through the other supplies
This means you'll have current constantly flowing through the steel structure which can lead to all sorts of issues, possibly including accelerated corrosion of the steelwork
 
Thank you, I had not considered the higher current in the good PEN, I must look as the building I work in has 3 or 4 supplies, there were separate units, but now are all combined and the cost of having supplies removed exceeds the cost of the standing change by a huge amount, so they were left in, although lightly used.

I was told it was PME and that the EV charge point has it's own earth rod, but never really looked as had no need to.
 

Reply to Steel framed units multiple PME supplies in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi guys, Have a job on next week for a friend, my usual industry is maintenance so want to be sure I am checking all the boxes here. He...
Replies
53
Views
5K
Hello Guys I have a 200a 3-phase supply PME bolted to a large ryefield panel, the ryefiled panel then supplies 14 flats within the same building...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock