DickiePhitt

Let me say from the off that although I'm electrically competent I'll be getting a professional in to do the work. I just like to know the answers before I ask professionals questions!
So I have a 100A single phase domestic supply feeding the house CUs as well as a CU for an EV charger. One of the CUs feeds an AC coupled Inverter & battery.
The EV charger and the EPS on the inverter are earthed via a TT Island.
There is a 100A dual pole switch between the meter and the Henley Block feeding the CUs.

Would the correct level of surge protection for the house be provided by replacing the 100A switch with something like this Wylex100A DP Isolator with type2 SPD?

 
Do you have overhead lines or a lightning protection system?
 
Assuming there's a comma missing and you have underground cables it sounds like a type 2 SPD would be the right choice. If possible, I would recommend having it in the consumer unit instead. Generally, a DP isolator can be purchased from £20 and a SPD under £50 but as a retrofit I see nothing wrong with the wylex one.
 
Yes missing comma!! Thankyou. By the time I've covered off 3 CUs I don't think there will be much in it cost-wise. Maybe even cheaper by the time labour factored in.
 
  • Like
Reactions: Aaron b

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Surge Protection Advice
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
DickiePhitt,
Last reply from
DickiePhitt,
Replies
4
Views
1,542

Advert